MicroLogix1000 Outputs not working But has indication

Carbon Fibr

Member
Join Date
May 2014
Location
Ontario
Posts
24
Hi all.
Ive made a small I:0/0 push button and a O:0/0 light program to test that my plc is working.

I got the bush button on a 24VDC and the light I've tried AC and DC always stays on or other outputs will just stay off.

In the program the pushbutton activates on the screen than makes the output true, the indication of output light turns on the PLC itself but the actual switching doesnt work.
Also i've done a continuity test between VDC and O:0/0 and their the same point? wha?
Its a 1761-L20BWA-5A

Any help would be appreciated thanks.
 
Last edited:
Sounds like the contact on O:0/0 welded shut. Is this a new PLC or a used one? If new, I'd try to return it under warranty. If it's not, then there was probably a power surge at some point in its life that welded the contacts together. If a relay contact is staying closed even when power is off, then the output is bad.
 
I do not believe its welded closed, every output is giving me trouble.
Also when the PLC is de-energized the continuity between the VDC/VAC O:0/0 is not the same anymore.

I cant get one output to "switch" using a multimeter to test after changing output in the program once each output is energized.
 
Please attached a sketch of how you wired everything up, including the input wiring, and external power supply if used
 
You said you have checked continuity, have you checked the voltage at the output?
What is the voltage rating/requirement of your output (light)? Have you checked voltage acrossed it?
 
Last edited:
yeah :( The outputs are not sending any voltage out once energized, Its also 24VDC light and it does turn on; its not the light. That is for O:0/1, the light for O:0/0 is always on.

For some reason O:0/0 and O:0/7 are normally closed which are sending voltage without the output being energized. But when i De-Energize the PLC O:0/0 and O:07 become normally open.
 
Last edited:
Little 24VDC light bulb. And a meter Yeah nothing big. Does the PLC require a big load to actuate the output??
My knowledge is that the vdc I input into the port beside the output will energize the output once switched from the program. That being said the output should now have 24VDC coming out no matter the size of the load.
 
quick observation, is your ground terminal grounded??, your wiring looks fine expect for the ground connection, it should be grounded. When you measure the voltage between O/1 output and 24vdc common you should get 24volts DC. Also as Mickey suggested what is the rating for your Light? i know you said its 24vdc, but at how many amps, i doubt you used a light bulb which pulls high amperage, but you never know
 
It is not grounded, what would the ground have to do with it? Also the light turns on with the voltage applied doesn't show an amperage ratting. Also measuring voltage between O/1 and common of the DC is no voltage. I do know if it does actually work which is what I'm trying to make happen, is the pin O/1 and 24VDC - will have 24VDC.
 
Is there something in the PLC that makes all outputs not work? Even though I'm getting output indication?
Also anyone got an answer to should I hear anything within the PLC once an output is energized?
 
I think a 24V DC light bulb should be enough of a load, I think that you need 2.5 mA min. at 14V dc
Sometimes I get tripped up when I don't see a voltage when checking with a meter only.
 
Based on you part number 1761-L20BWA-5A, the BWA, the B represents that all inputs are 24VDC, the W means that for the Outputs they are relay outputs, so when the specific output is energized you "should" hear the relay pull in.

As for Grounding although it doesn't seem to be the culprit of the problem, i got this from the manual "
All devices connected to the user 24V power supply or to the
RS-232 channel must be referenced to chassis ground or
floating. Failure to follow this procedure may result in
property damage or personal injury.
Chassis ground, user 24V ground, and the RS-232 ground are
internally connected. You must connect the chassis ground
terminal screw to chassis ground prior to connecting any
device"
 

Similar Topics

Working on a machine that uses an Allen Bradley micrologic’s 1000 controller. Wondering if there is away to tie in the output to an external...
Replies
14
Views
2,936
Hello, i made a program in rslogix500 for my micrologix1000 plc. can i import this program into the CCW software then convert the program which...
Replies
1
Views
1,494
Could someone please guide me in the right direction? I currently own a 1761-L32BWB (Micrologix1000 processor) and a 1761-CBL-PM02 (programming...
Replies
15
Views
4,519
Ihave a machine with a failed Moeller PLC that I have no documented logic for, and am replacing with a micrologix 1000 1761-L20BWB-5A. Most of my...
Replies
14
Views
3,394
Hello, Have a ML1000 communication via NET ENI module to a PanelView Plus 600 HMI running Ver3.1 firmware. In my FTView 6 I've created and on...
Replies
4
Views
1,960
Back
Top Bottom