slc5/04 FLT light blinking

muds

Member
Join Date
Apr 2014
Location
karachi
Posts
71
hi

i want to discuss one issue that on my allen bredly slc5/04 1747-L541 cpu FLT fault light blinking appears,,,i want to re-programme this cpu with backup of my programme...but iam unable to communicate with this cpu,,i am using 1747-AIC driver in rslinx to go online with normal cpu and using serial pot of my cpu for communication,it work fine for other cpu for programming.
but in this fault appearing cp, iam unable to go online and fault appears that 'no response form processor or node adress?
where iam wrong??please help me on this

THANKS IN ADAVNCE

Untitled1.jpg
 
Last edited:
Are you able to get connected with RSLinx? This would be the first step.

Does your PC have a real serial port? What cable are you using. (Null-modem)

Do you have the offline file? If so post it here (zip it first). This will help us determine how the serial port on your SLC is configured.

If you don't need the program that is in the SLC now you could clear the memory, which would set the comm ports to there default settings.

DF1 protocol on its serial port.

See pdf's below for how to clear the memory and set up RSLinx to communicate with the SLC serial port set for DF1 protocol.
 
Last edited:

Similar Topics

I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,584
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,299
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
656
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
943
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
Replies
3
Views
993
Back
Top Bottom