How to do addressing of 1794-IB32 module.

makarand3105

Member
Join Date
Jul 2014
Location
Mumbai
Posts
2
Hello All,

I want to do addressing of 1794-IB32 (32 input) in RSLogix5 (PLC5).
How it should be? addressing is staring from I05000.

Will it be? I05000-I05008
I05010-I05018
I05020-I05028
I05030-I05038


Regards,
Makarand
 
Aye, and PLC5 addresses generally do not have an "8"

0 to 7, 10 to 17 etc etc

If you have said that it is rack 5 group 0 module 0 and it is 1/2 slot addressing, then it may well become :

I:050/00 to I:050/07, I:050/10 to I:050/17
and
I:051/00 to I:051/07, I:051/10 to I:051/17
for the 32 channels...

I would need to check on one my PLCs to confirm
 