I am troubleshooting a Panelview and CompactLogix PLC.

I want a communication fault alarm to be indicated in the HMI when the communication cable is disconnected.

Right now, the alarm tag used for the comm. fault is [PLC]@connectionsdropped.

Sometimes the alarm tag is not working.

Does anyone know how this tag work?

Do you have other suggestion for the comm. fault indication alarm?

Thanks in advance.
 
Instead, use [PLC]@IsPresent.

@ConnectionsDropped is a statistical counter the describes the underlying CIP protocol behavior.
 
Thanks Ken,

I will try to test that one out.

By the way, do you have any manuals regarding this kind of tags? the @xxxx one. It's my first time encountering them. I am having a hard time searching about these tags in the net.
 

Similar Topics

I have a problem and I can't find anything about it in the Rockwell Knowledge Base. The problem is that I am losing communication with a...
Replies
1
Views
1,251
Dear All. I need comm between Compactlogix/Controllogix with PNOZ m1p ETH. What we need the communication option? or can be connect direct? many...
Replies
0
Views
1,190
I have a Compactlogix PLC connected to a Toshiba P9 (ASD-G9ETH Module) via ethernet that is working perfect while I have the laptop connected to...
Replies
1
Views
1,695
I have a ML 1400 that will be talking to a CL L18ER. N13 is data to be sent from ML to CL and N14 is data from CL to ML. The CL is utilizing SLC...
Replies
2
Views
2,955
I have 20 REAL values that I need to get from a 1769-L30ER (v24) to a 1769-L32E (v16) via Ethernet. They are both on the same network and I tried...
Replies
7
Views
2,087
Back
Top Bottom