NEC Article 100 - Continuous Load and duty cycle

bimmersix

Member
Join Date
Jul 2014
Location
PHX, AZ
Posts
38
I am looking for clarification on the definition of "continuous load" for the purpose of sizing conductors and overcurrent devices. Some components are quite obviously one or the other...

What if you have heating elements that keep a process at temperature, but rarely exceed 50% duty cycle (solid state switching) except at startup - which is <30 minutes?

I was unclear whether "3 hours of operation per day" means a continuous 3 hours or a sum of three hours and if duty cycle even factors into these calculations. Any input is appreciated. Thanks,
 
bimmersix,

i would say that heating elements are continuous because they are solid state controlled. My opinion.

you must also consider the number of conductors (derating factor), ambient temperature (derating factor), terminal rating (this rates the wire amperage reguardless of what you use), type of wire, location, and other things as well.

regards,
james
 
bimmersix,

i would say that heating elements are continuous because they are solid state controlled. My opinion.

you must also consider the number of conductors (derating factor), ambient temperature (derating factor), terminal rating (this rates the wire amperage reguardless of what you use), type of wire, location, and other things as well.

regards,
james

Thanks, James.

Yes, I have factored those in (6 conductors in a raceway, 75C terminals, 50C ambient). I am using MGT 450C wiring. As we speak I am reading and highlighting through the entire NFPA 79 (2015 Edition). I'll probably need to visit NFPA 70 and at least NEC 240.
 
Personally I'd call the "<30 minutes" 100% load warm up continuous for sizing purposes. Especially with a 50*C ambient and 75*C terminals. Not a whole lot of margin for error there.
 
You need not look any further than NFPA70 Article 424.3(B)

Which states:

"Fixed electric space heating equipment shall be considered continuous load"

BCS
 
Last edited:

Similar Topics

Does a hardwired 120 VAC machine need a local disconnect and lock out device? I was always under the impression that it did, but a plant controls...
Replies
4
Views
2,099
Replies
7
Views
2,133
Hi I have a Sinec H1 card with both the run and stop lights currently illuminated. The CPU is in Run. Just got handed this and no idea what...
Replies
6
Views
1,562
I have some reservations about a design I am working on. The customer has a fan motor that is mounted away from everything on a mezzanine. It...
Replies
5
Views
1,597
There are many threads on this forum discussing the matter of using one circuit breaker for protection of several motors, servodrives of VFDs...
Replies
2
Views
1,340
Back
Top Bottom