Problem adding CIP drives offline, missing something easy.

CapinWinky

Member
Join Date
Aug 2011
Location
Virginia
Posts
566
I'm trying to add some Kinetix 6500s to an EN2T and when I create a new axis from the drive properties window, I get this prompt:

"The axis cannot be associated to this module. The CIP Motion Drive module requires Hard or Soft Time Synchronization, and the parent scanner is not configured to support it."

The controller has "Enable Time Synchronization" checked and the EN2T doesn't seem to have any settings in its properties that I can adjust that are related to CIP Sync.

I've tried creating a new axis from the drive properties and manually creating a CIP axis and mapping it both from the drive properties and the axis properties. The error generated from the axis properties is different wording but the same message as the one above, specifically saying the EN2T is not configured with "Time Sync Connection".

What am I missing? Do I have to go online to get the EN2T to populate with CIP Sync data?
 
Check which processor/firmware version you have set. The controller must support CIP drives as well. Revision of the EN2T may be an issue as well.
 
Did you ever find an answer? I had the same problem trying to configure a Kinetix 350 through a 1756-EN2T. I found that under the properties of the 1756-EN2T, General tab, I had to click "Change..." button in the Module Definition section, and then set the Time Sync Connection to "Time Sync and Motion".
 
Did you ever find an answer? I had the same problem trying to configure a Kinetix 350 through a 1756-EN2T. I found that under the properties of the 1756-EN2T, General tab, I had to click "Change..." button in the Module Definition section, and then set the Time Sync Connection to "Time Sync and Motion".

That is the right solution. I found the same answer on this document from Allen-Bradley.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/motion-um003_-en-p.pdf
 

Similar Topics

Hello I have a two controllers 1756-L61 and I would like to add an Ethernet Card module of one controller to the other one. When I search for...
Replies
6
Views
881
Hello All, Thanks in advance... Friends today I am adding a New EthereNet Module ENBT through RSLogix 5000 software..but after adding details...
Replies
4
Views
3,807
Hi, There is a compare block being used 1100 times to compare variables to a constant value -999. The problem is that the GE is changing the -999...
Replies
2
Views
1,859
Hi all, I just added an ACN to my network which already has 10 ACNs. After adding ACN with 2 Inputs and 2 Outputs, I opened RS networx and the...
Replies
9
Views
3,208
I have a control logix network with a Logix5555 controller along with eight CNB modules at remote locations. Each remote location has various AI...
Replies
6
Views
4,424
Back
Top Bottom