Hello
I have a two controllers 1756-L61 and I would like to add an Ethernet Card module of one controller to the other one. When I search for the controller L61 in the list I don't find it. My list begins with the L81 controller.
Any help please.
Thank you.
Hopefully I'm not misunderstanding, but for control logix, you add an Ethernet module first, then under the Ethernet module, you add the controller. The likely reason you only see L8 series controllers is because they have a built in Ethernet module, where the other controllers do not
I have an Ethernet module configured with my first PLC in my project, and I try to add the controller L61 to that ethernet card. My version of RSLogix is v20.
can the version be a problem?
Thank you.
I added an 1756-ENBT and added my remote controller L61, but when I go online it gives me an error (communication failure). I have the correct IP of the card. I don't know what is the problem.
Problem solved. Finally it talkes to add the controller with a right version of a cpu and a right number of slots.
regards
Neither the number of slots nor the firmware version matters.
Be sure that your connection to the remote 1756-ENBT is not a "Rack Optimized" connection but rather is set to "None", so that it serves only as the structure for the Producing CPU object. That will remove any rack-size related connection errors.
Hello All, Thanks in advance... Friends today I am adding a New EthereNet Module ENBT through RSLogix 5000 software..but after adding details...
3,807
I'm trying to add some Kinetix 6500s to an EN2T and when I create a new axis from the drive properties window, I get this prompt: "The axis...
4,945
Hi, There is a compare block being used 1100 times to compare variables to a constant value -999. The problem is that the GE is changing the -999...
1,859
Hi all, I just added an ACN to my network which already has 10 ACNs. After adding ACN with 2 Inputs and 2 Outputs, I opened RS networx and the...
3,208
I have a control logix network with a Logix5555 controller along with eight CNB modules at remote locations. Each remote location has various AI...
4,426