Hi,



I just want to connect multiple 485 scanner to a 1734 -485 asc module....Is it possible that 1734 asc can support multiple slave connection,,,



If not can some tell me which Comm module for Compact logix support this option..



Regards,

Nelliyan.G
 
I remember from one of your other posts that in this case a "scanner" is a barcode scanner with an RS-485 connection.

Because RS-485 is a multi-drop electrical network technology, it is definitely possible to use multiple devices on a single RS-485 network.

The question is whether or not the protocol used by the barcode scanners is appropriate for a multi-device network.

If they are just sending out ASCII strings without being "polled" by a master device, there may be no automatic way to prevent multiple barcode scanners from transmitting at the same time, which would make the data corrupted. Making sure that only one scanner transmitted at one time would be a system configuration or function issue.

Or, if the barcode scanners do not identify themselves when they transmit, it may be more difficult to tell which scanner has transmitted.

Your other post made it sound like you are trying to use a controller that is too small, or avoid buying the appropriate I/O modules to perform the functions your system needs. I can't really give you advice other than to use a controller that has enough module capacity to perform the functions of the control system.
 

Similar Topics

Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
31
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
16
Views
530
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
225
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
346
Hi all, This is my first time working with a 1734-IE2C analog module. I am tasked with wiring the flow meter into the analog card and the OEM is...
Replies
2
Views
165
Back
Top Bottom