PanelView 600

jayala

Member
Join Date
Jun 2004
Location
CA
Posts
17
HI
I just purchase an AB Panel View 600 CAT# 2711-T6C5L1 I have been trying to communicate with it using cable 2711-N13 no luck when I turn the Panel View on it shows DH485 on the screen also I don't know if 2711-N13 cable it's for communication between PLC & Panel View or if it can also be use to program the Panel View? Which driver do I need to use? I was using DF1 driver the reason that I used DF1 is because it Shows DF1/485.I really don't know if I have the right cable,driver.Any help will be very apreciated.
THX,.
 
Hi, your 2711-T6C5L1 uses DH-485 protocol, but implemented on a point to point RS-232 physical connection.

This means you will need to set RSLinx to the 1747-PIC/AIC+ DH485 driver and connect directly to the PC COM port.

Similarly the connection to the PLC will be point to point and the Ch0 port will need to be configured to DH-485 with the correct baud rate (usually 19.k) and a unique node address.

If you want to program the PLC and the PanelView via the same connection you will either need to set up a 1761-AIC+ to allow multiple nodes on the DH-485 segment, OR set up the Pass-Thru functionalilty of the PLC processor and connect to the PanelView from the other port on the PLC (ie DH+, Ethernet)

The 2711-Nc13 is the correct cable.
 

Similar Topics

I am trying to go to a 504 CPU. and on my hmi I am getting a 9028 error. can someone explain what they mean by change reference?
Replies
12
Views
220
Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
462
Hello, Friends Please someone help me find right cable to communicate Panelview 600 (2711-B6C9) to Micrologix 1200 (1762-L24AWAR). AND any advice.
Replies
3
Views
271
Hello , I have an HMI of PV+ 600 (2711-T6M5D) Ser A Rev B, This HMI doesn't have the ethernet port i have to take backup through communicate...
Replies
5
Views
653
Hello all, I copied the MER file from one PanelView Plus 600 to another one, using a USB drive. On the new HMI, I copied the MER file to the...
Replies
4
Views
628
Back
Top Bottom