Hello ,

I have an HMI of PV+ 600 (2711-T6M5D) Ser A Rev B, This HMI doesn't have the ethernet port i have to take backup through communicate RS232. Which cable i have to use? In RSlinx which driver i have to select?

Can i use the cable USB-2711-NC13 for RS232 communication?


I am new for AB brand,

Thanks in advance.
 
Why not use a USB flash drive to back it up?


EDIT:


While I've never used it for panelviews, you should be able to use that cable to communicate to it according to this manual:
https://www.rockwellautomation.com/en-us/products/details.2711P-T6M5D.html


Then to set up your driver in RSLinx, set it up as a RS232 DF1 driver, select your Com port, then for device type, select "SLC-CH0/Micro/PanelView", then click "Auto-Configure" and it should set up everything else for you.


Hope that helps.

2023-11-21 08_16_43-Windows 10 LTSC - VMware Workstation.png
 
Last edited:
Why not use a USB flash drive to back it up?


EDIT:


While I've never used it for panelviews, you should be able to use that cable to communicate to it according to this manual:
https://www.rockwellautomation.com/en-us/products/details.2711P-T6M5D.html


Then to set up your driver in RSLinx, set it up as a RS232 DF1 driver, select your Com port, then for device type, select "SLC-CH0/Micro/PanelView", then click "Auto-Configure" and it should set up everything else for you.


Hope that helps.
I used the USB but it didn't detected, i connected my USB, the external storage was not shown. i don't know why?

Also, i tried with folder path, it didn't shown. Also tell me the solution for this?

thanks for the reply.
 
It could be. Maybe try formatting it as a smaller partition or using a smaller USB.


Otherwise, you should be able to backup the running program on the PanelView by setting up the RS232 driver as I explained above and then using the FactoryTalk Application Manager to upload the program.
 

Similar Topics

Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
Replies
10
Views
466
Hello all, I copied the MER file from one PanelView Plus 600 to another one, using a USB drive. On the new HMI, I copied the MER file to the...
Replies
4
Views
629
Hi all, I have an old PanelView Plus 600 (2711PC-T6C20D8) that I am repurposing on our site - I have flashed the firmware to ME version...
Replies
4
Views
980
Hello Team, I have a question, I have been working with a panelview plus 600. But I have deleted all the .mer directly from the HMI, after that I...
Replies
16
Views
1,703
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
Replies
1
Views
736
Back
Top Bottom