Hello ,
I have an HMI of PV+ 600 (2711-T6M5D) Ser A Rev B, This HMI doesn't have the ethernet port i have to take backup through communicate RS232. Which cable i have to use? In RSlinx which driver i have to select?
Can i use the cable USB-2711-NC13 for RS232 communication?
I am new for AB brand,
Thanks in advance.
Why not use a USB flash drive to back it up?
EDIT:
While I've never used it for panelviews, you should be able to use that cable to communicate to it according to this manual:
https://www.rockwellautomation.com/en-us/products/details.2711P-T6M5D.html
Then to set up your driver in RSLinx, set it up as a RS232 DF1 driver, select your Com port, then for device type, select "SLC-CH0/Micro/PanelView", then click "Auto-Configure" and it should set up everything else for you.
Hope that helps.
EDIT:
Hope that helps.
I used the USB but it didn't detected, i connected my USB, the external storage was not shown. i don't know why?
Also, i tried with folder path, it didn't shown. Also tell me the solution for this?
thanks for the reply.
It could be. Maybe try formatting it as a smaller partition or using a smaller USB.
Otherwise, you should be able to backup the running program on the PanelView by setting up the RS232 driver as I explained above and then using the FactoryTalk Application Manager to upload the program.
Hi I have a number of the older PanelView Plus 600 HMI's (2711P-T6C20D, Ser D) that I want to update to the latest firmware. I believe that the...
497
Hello all, I copied the MER file from one PanelView Plus 600 to another one, using a USB drive. On the new HMI, I copied the MER file to the...
650
Hi all, I have an old PanelView Plus 600 (2711PC-T6C20D8) that I am repurposing on our site - I have flashed the firmware to ME version...
1,002
Hello Team, I have a question, I have been working with a panelview plus 600. But I have deleted all the .mer directly from the HMI, after that I...
16
1,762
Every time I power this unit up it loses its IP address and goes to DHCP . When I goto the config the IP address is 0.0.0.0
752