panelview plus 700 and dh+

Jim Cavanaugh

Member
Join Date
Jan 2004
Location
south Jersey
Posts
5
I have a slc 504 with dh+ and three panelview plus 700. When i connect two touch screens that have the same program app, they work fine when i connect the third screen i get a legacy message (error) that pops up on all three screens. it does not matter which two screen are connected they work fine when the third screen is connected the network goes down. any ideas.

jim cav
 
[QUOTE]Originally posted by Jim Cavanaugh
I have a slc 504 with dh+ and three panelview plus 700. When i connect two touch screens that have the same program app, [/QUOTE]


:) They have different node addresses I hope........ :)
 
So then...

How is the network wired... Trunkline with droppers to each node?? or daisy chained??

Are the correct terminating resistors used for the given baud rate ??
 
What does that error message say exactly ?

Maybe its is the SLC5/04 that cannot handle so much communications.
Try to insert a few SVC (Service Communication) instructions in the SLC program.
And/or try to reset S:2/15 (Comms Servicing Selection).
Notice: Both actions will increase the scan time of the SLC5/04.
 
Are you sure the node addresses are different? There are some settings related to the terminal starup that could cause you to accidentally duplicate node numbers (replace network settings on startup). I have also had a similar occurence when I accidentally set a node to a different baud rate than the network. Also check termination.

Darren
 
On RSLinx do you see the processor and all 3 panelviews on the dh+ network. If you do it's not a node or baud rate problem. Could be related to the number of panelviews on the network. May need to increase your data read/write timeouts.
 

Similar Topics

My Panelview plus 700 HMI stopped working and I replaced it with a new one. Moved the sd card from the previously installed panel to this one and...
Replies
16
Views
993
Good day all! I need to make some modifications to a Panelview program. I uploaded it from the unit. Tried to use the Application mgr. to...
Replies
6
Views
1,090
Hi All. I am working on my home automation system again and i am looking at setting up a panelview. Currently running an AB Compactlogix...
Replies
3
Views
839
Hi. I'm working on a plant that has a panelview plus 700. Problem is that from time to time, the alarm list shows an old false alarm instead of...
Replies
10
Views
2,727
Back
Top Bottom