Hi everyone, I'm currently trying to comunicate a panelview 600 with a PLC 5/40. The PLC is connected to a powerflex 700 via RIO. What I wanna do is to activate the start and stop bits of the powerflex. Which should the tag address should be?
 
Wasn't most of your answer in the thread:
http://www.plctalk.net/qanda/showthread.php?t=92241

Ken Roach says:
The PanelView is emulating an I/O rack itself. Your addresses have to apply to that I/O rack.

You can ONLY address the 'rack address' associated with the PanelView

Geospark provided additional support to that subject and you need to pay attention to the help people have provided you.
 