[FONT="]I need to connect a TOC analyzer digital output alarm to a PLC. I totally believe that it is intended for that. My confusion comes from reading the manual – of course. The manual has the picture and words shown in attachment manual.png. How I would normally connect an alarm switch is shown in N1.png. Does my normal method look right? [/FONT]
[FONT="] [/FONT]
[FONT="]I know a transistor switch can have a very small current capacity (8.5mA), but I am also confused by the plus & minus signs in the manual. I would be connecting it opposite of that. In the manual, the +Voltage goes to the relay which then has its common sent to the COM on the analyzer. Since I will be using an external voltage, it will be different but I wonder if I will be connecting it backwards. [/FONT]
[FONT="] [/FONT]
[FONT="]Is a PLC input just an open collector with the drain connected to PLC COM? [/FONT]
[FONT="] [/FONT]
[FONT="]I looked up the current requirements for the Micrologix digital inputs and found.[/FONT]
[FONT="]On-State Current for the 1763-L16BWA:[/FONT]
[FONT="]minimum 2.5mA at 14V dc (for inputs 0 – 3)[/FONT]
[FONT="]nominal 7.3 mA at 24V dc[/FONT]
[FONT="]maximum 12.0 mA at 30V dc[/FONT]
[FONT="]I also see that input impedance is 3100 ohms/input which equates to 7.7 mA at 24V[/FONT]
[FONT="] [/FONT]
[FONT="]So I am confident that I can connect the output to the PLC, but not sure if I am doing it right.[/FONT]