[FONT=&quot]I need to connect a TOC analyzer digital output alarm to a PLC. I totally believe that it is intended for that. My confusion comes from reading the manual – of course. The manual has the picture and words shown in attachment manual.png. How I would normally connect an alarm switch is shown in N1.png. Does my normal method look right? [/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]I know a transistor switch can have a very small current capacity (8.5mA), but I am also confused by the plus & minus signs in the manual. I would be connecting it opposite of that. In the manual, the +Voltage goes to the relay which then has its common sent to the COM on the analyzer. Since I will be using an external voltage, it will be different but I wonder if I will be connecting it backwards. [/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]Is a PLC input just an open collector with the drain connected to PLC COM? [/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]I looked up the current requirements for the Micrologix digital inputs and found.[/FONT]​
[FONT=&quot]On-State Current for the 1763-L16BWA:[/FONT]​
[FONT=&quot]minimum 2.5mA at 14V dc (for inputs 0 – 3)[/FONT]​
[FONT=&quot]nominal 7.3 mA at 24V dc[/FONT]​
[FONT=&quot]maximum 12.0 mA at 30V dc[/FONT]​
[FONT=&quot]I also see that input impedance is 3100 ohms/input which equates to 7.7 mA at 24V[/FONT]​
[FONT=&quot] [/FONT]​
[FONT=&quot]So I am confident that I can connect the output to the PLC, but not sure if I am doing it right.[/FONT]​

Manual.png N1.jpg
 
The manual shows a sinking output. Its connection from the 'outputs' to the 'solid state relay' shows how it should be used.

You should connect the + voltage of the power to the 'DC COM' terminal of the PLC. (I believe each group can be wired either way.) The 'OUT' from the unit would then connect I/x of group '0'. Note that, with the common of the group wired to + then all 4 inputs are required to be of the 'sinking' type.

Your 'N1' diagram is showing a type of 'sourcing' device hook-up.

The Micrologix DC inputs circuits are connected, on one side, to the common terminal of its group. But the circuits of a group can operate in either the 'sourcing' or 'sinking' mode.
 
Last edited:

Similar Topics

Dear All, Related with the autem plc analyzer, I have one problem with the ethernet communication, i would appreciatedif you support to me...
Replies
0
Views
7,674
Disclaimer: English isn’t my native language, so apologize for any incoming grammatical or spelling mistake. Hello everyone. I’m trying to make...
Replies
3
Views
2,201
Hello PLC experts, I have a question for those of you familiar with studio 5k. A moisture analyzer was added to the PLC as a REAL data type tag...
Replies
15
Views
5,247
We installed a pH control system in our wastewater system. pH probe report to a Rosemont analyzer and send a 4-20 signal to our controller and...
Replies
16
Views
4,945
I have Frontline NetDecoder Software and a 1784-U2DN in hopes of troubleshooting a DeviceNet issue. Randomly we have Nodes that stop communicating...
Replies
7
Views
2,469
Back
Top Bottom