I have (2) L541 5/04 PLCs in the plant and up until 3 days ago they were fine. I replaced the battery in one of them and had to reload the project. When I attempted to download, it failed with errors - ERROR: FBC instruction is not valid on the currently selected processor!-> 1747-L541 5/04CPU - 16K Mem. OS401. Both of the SLCs have FBC instructions in the ladder file and have for several years. I am running linx 3.51.01 CPR 9 SR 5.1 and Logix 500 9.00.00 (CPR9). Has anyone seen this anomaly? Any help greatly appreciated!
 
Make sure the firmware level of the L541 matches the RSLogix configuration.

I seem to remember running into something similar in an older version.
 
Problem Resolved

The L541 does not support FBC Instructions, but the L541C does. The selected controller in the properties tab was L541 (not C) it must have been changed at some point. I changed it to an L541C in the offline file, put the FBC Instruction back in the logic and was able to download with no errors.
 

Similar Topics

I'm trying to remember the lessons for replacing a SLC CPU, but I so rarely have to do it, I'm afraid of screwing it up. I'm hoping to give my...
Replies
6
Views
2,481
Hello fellas... Been a long time. I'm currently stumped. O:6/8 comes true (on) at every power cycle. For the life of me I can't figure out why. I...
Replies
6
Views
2,362
Having a problem with is processor PLC SLC 500 cat:1747-L541, the fault light is flasing and cannot go online and again the DH+ comm. is flushing...
Replies
2
Views
1,791
I have one SLC-1747 L541 controller.when i tried to communicate with my computer through RS 232 and USB adaptor,an error msg is coming like "check...
Replies
4
Views
1,974
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
Replies
5
Views
544
Back
Top Bottom