OMRON PLC trouble

sronggot

Guest
S
Dear sir,

I have omron PLC CQM1H, but i have trouble. The led lamp for comm indicator always lit, and the run indicator not lit. so the Output of PLC can not operate ?

anyone cab tell me to solve that problem ?

thanks for your help.

best regards,

didi
 
Omron Startup Mode

If you can get online, ensure that the PLC Setup, Startup option, is set to "RUN" or "MONITOR", not "Programming Device".

If it's set to the latter, and if you've something like a CIF01 plugged into the periph port, when you power up, the PLC starts in PROGRAM mode.
 
I believe that the "comm" led is lit if any programming device (laptop, etc.)is plugged in, or if you have any serial device (touchscreen, etc.) plugged in.
For the "run" LED to be on the PLC needs to be either in run or monitor mode. I think Omron calls it the "operating mode". If your using CX Programmer, go under the "PLC" pull-down menu to change it's setting.

OR...

CTRL + 1 is Program Mode
CTRL + 3 is Monitor Mode
CTRL + 4 is Run Mode
 

Similar Topics

Hello Sir/Ma'am, Hope you and your family are safe in this Covin-19 Pandemic. One of my client have a machine in their ceramic industry which...
Replies
0
Views
2,629
Hi, I am using Omron sysmec plc & it cant work & show indication Memory Error. pls Tell me what should i can do remedy. Thanks,
Replies
1
Views
3,032
S
I am working on a machine that has 4 omron plcs connected to each other. The 'master' is a C200HS where as the other 3 are CQM1's. I can upload...
Replies
9
Views
7,310
I've come across a system running omeron cx-programmer version 9.42. Am I going to need to find a legacy version of the software to edit and...
Replies
1
Views
70
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
4
Views
171
Back
Top Bottom