Hi there,

Could someone explain how does de Input and Output Modules works.
I am using a 1771 IAD 120 AC/DC Input Module with a PLC5 Allen Bradley.

I am new with this. Does the Input Module has to be grounded or it is already grounded with the Backplane or trough de PLC? The last terminal of the Module is called "L2 Low return" I dont know what this means.

I wired a simple button with 120 VAC. One wire to the 120VAC supply and the other wire to the Input Module but I think the ground wire is missing, Is it?
 
If you don't know what "L2" means I would recommend you get some help. 120VAC will kill you.

Having said that, as rootboy said connect "L2" (terminal E) to the neutral side of your AC power source.
It may or maynot be grounded.
 
Last edited:

Similar Topics

Has anyone ever calibrated an analog Input module for a PLC5? Was it worth the effort? I have a REV C 8 channel input module in a new project...
Replies
16
Views
6,999
Hi guys, I've an new aplication to be added into the existing system where the sensor will send 2000 pulse/signal to the PLC-5/60 in every...
Replies
12
Views
5,574
I've got a 4-20ma pressure transducer connected to an analog card on an AB PLC5. Under the setup for the card, I have to set a raw minimum and...
Replies
12
Views
7,411
Hopefully this is fairly clear cut. I need to get a 4-20mA signal added to an I/O module of a PLC5 40 E. Using RSLogix5. There already is an...
Replies
14
Views
4,906
PLC5/80 RSLogix5 7.40.00 (CPR 9) Is there any way to search for a forced input in the find dialog? I know you can view the force tables but need...
Replies
4
Views
2,724
Back
Top Bottom