Hello everyone, I have a PowerFlex 70 that is controlled by a 1756-L73 controller via a 1756-DNB and 20-COMM-D module. DigIn 1 Sel (parameter 361) is set to "1 - Enable" The 24VDC comes from the drive, through a pull cord, and back up to terminal 1 on the drive. I would like to monitor the value of DigIn 1. I am wondering if there is a way to do this over the network or if I would have to wire it up separately to a 1756-IB16I.
 
This should be relatively easy.

On the PowerFlex 70, Parameter 216 is the raw values of the Digital Inputs.

You can add that to a DataLink, which will require a re-configuration of the I/O connection and re-mapping in the 1756-DNB scanlist.

Or, you can send Explicit Messages to the Parameter object in ladder logic.

This would be a "Parameter Read", which is Service 0x0E hex (Get Attribute Single), Class 0x0F hex(Parameter), Instance 216 decimal (Digital Inputs), Attribute 0x01 (Value). The MSG block will gray out everything but the Instance field when you select "Parameter Read" as the service.
 

Similar Topics

Is there a way to pull the heatsink temp from parameters to the PLC? I've had a couple critical drives fault recently for failed heatsink fans. We...
Replies
2
Views
2,168
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
51
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
117
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
106
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
100
Back
Top Bottom