16#0002 Resource unavailable
Oct 2015
Melbourne
23
Howdy.
Have compact Logix with a SM-2 module installed, talking MODBUS out all three channels to various aftermarket devices. Been in and working rock solid for several months.
Recent torrential rains have caused issues, underground comms cables failed, in turn failing aftermarket MODBUS devices. Over a few days of testing and replacing both cable and devices, all appeared to be working again, then without warning all MODBUS comms stopped.
Error:
16#0002: Resource unavailable.
I cannot seem to get it to work, I have (accidentally) put PLC into Program mode then back to Run mode, no help. I am waiting for after hours to be able to cycle power to entire system.
In the meantime, would anybody have any tips on what to look for/do?
Thanks.
Well, turns out a hard power cycle fixed it. Can't explain, but suspect something along the lines of a few days generating errors and the poor machine said ENOUGH!
I've not seen any sign of those torrential rains you speak of around these parts. You're not a Queenslander in disguise are you?
That error code and message has a few entries in the knowledgebase, but all of them would seem to apply to something that was incorrectly set up from the get go and would never have worked. In your situation I'd have done exactly as you described - cycled the power, shrugged, and chalked it up to a magic smoke error.
Anyone have those mentioned gsd file. Plase share, i do not know what the type of that profibus dp slave.
44
Hello everyone, I've came across problem with safety I/O modules. In my project we have 66 same systems and every system use same hardware, so...
3,072
Just got back from a customer with an L40C (SER C, FRN 6) that immediately faults at powerup. I can download the program, switch to RUN, and it...
1,667
HI, WHEN THE MACHINE RUNS AT 50% EVERYTHING RUNS WELL.BUT WHEN WE RUN THE MACHINE AT HIGHER SPEED,THE MACHINE WILL RUN FOR A WHILE THEN...
5,066
Greetings. I was installing a 1746-NIO4V in an unused slot (7-slot rack) to support a new project. The processor is a 1747-L541 with DH+. Dip...
2,706