reverse three phase to reverse rotation
lesmar96
May 2017
PA
520
Hey, this might be a simple question, but I don't think I ever ran into it before.
We all know that on 3ph, any two leads can be swapped to switch the rotation of the motor. Does this not work through a vfd? I suppose with the DC bridge, etc. the output phasing is not necessarily sequential with the input phasing.
At any rate, today I had wired up a panel with a couple vfds and all the motors went the wrong way. Normally, i switch the leads in the terminal box, but since all the motors were going the wrong way, I thought I would just try to switch two leads at the incoming power disconnect. Well that didn't make any difference. Swapped two leads on the line side of the drive and they still went backwards.
Is that normal?
Yes, it's normal. The VFD input section (converter) turns that 3 phase into DC, charges up a capacitor bank like a battery, and then the output section turns it back into 3 phase with no real regard for the input section.. This is great since as long as you keep the wires between the drive and the motor straight, you don't have to worry about something happening to change the phase rotation upstream of the VFD. This is not so great if all your motors turn backwards because it means you have to go move a whole shedload of wires to make them right.
You can swap any two phases either at the Input, or Output of the VFD.
This can cause havoc if all the cables in the panel are identified "R, Y, B", people like consistence in the panel, it makes for easier maintenance.
So it might be better to swap the phasing at the motor terminal box, and update the field schematics accordingly.
Uhmm, no. Sorry to disagree, but swapping the input phases will have no effect on a VFD. It will work for a soft starter or for a mechanical motor starter... but not a VFD. You can only change rotation at the output side of the VFD.
Now one other way you can reverse them is through drive programming. That might be easier, but not necessarily the right thing to do.
Great answer, OkiePC. You are exactly correct. As for daba, unfortunately, you are exactly wrong for the reasons OkiePC cites.
Daba is sharp as a tack, so I BET he meant input to the motor... ;)
Yes, I said "Input" to the VFD by mistake, been a long day and didn't think it through.
Perhaps my sharpness is reduced by age, lol
The other considerations I think are valid, though.
Does the VFD in question have a Run FWD and a Run REV input? Or a direction parameter?
Telling the VFD to run a reversed motor in reverse would put the motion forward.
Yes. the vfd can run in either fwd or rev by terminal command, but I have been taught and also consider it not proper to run a vfd in Rev just to make the motor go the right way because that could cause confusion to some future person.
I don't think it matters. There is absolutely no concept of FWD/REV, versus Clockwise/Anticlockwise, etc.
Some manufacturers go with FWD or Clockwise when looking at the shaft, but there's a few that define FWD or Clockwise when looking from behind the motor.
I'm prepared to be shot down on this, but I don't think there's a "standard", especially when shopping "overseas".
I too stand to be corrected, but I always had the idea that FWD is the way something needs to go. For example, these were on conveyors that always needed to run the same direction and never go the other way. So I would have said that is fwd. Or an air compressor or blowers that needs to go a certain rotation, I would call in forward. But If equipment runs either or at any given time by system instruction, then there really is not fwd or rev per say. That was always my perception.......
Personally, I prefer to change as few drive parameters as possible from their default values. I'll connect the wires so as to make the motor turn in the direction I want it to go at the default direction parameter setting.
Logically speaking this makes the most sense in my opinion. When setting up several conveyors we used the default settings of the VFD, than swapped the wires on the output side of the VFD, if necessary. These conveyors were only designed to go in one direction...this was a company standard, and part of our buy-off procedure.
IEC 60034-8 and BS 4999 part 108 specify that the rotation direction is clockwise when viewed from the "Drive-end".
NEMA MG-1 specifies in Section 2.24 that the motor should rotate counter-clockwise when viewed from the non-drive end.
So they're the same, just from inverse definitions.
Go ahead, ask me when International Standards Day is.
If it were me, I would change the rotation at the local disconnect for the motor. This is a pretty standard practice, and should not confuse anyone. Plus it is a lot easier than rewiring the motor.
Bubba.
Hi all, I'm having trouble solving a problem I've been working on for several months, and thought you might like a stab at it. The machine runs...
22
1,073
I have a SX2 plc and i'm getting 0-10v analog signal,but i need 10bar analog output in 0v can someone explain how its done
567
I'm trying to add on to a safety circuit and trying to make sure this is fail-safe. My safety scanner needs some muting when things aren't running...
882
Hi, I have issue with acs800 starting the motor in reverse for like 5-6 seconds with a max speed of around -220 rpm before it goes to the...
2,049
I am looking at a 1305 drive connected to a PLC5 via RIO. The drive is working and I was able to get a functional HIM working on the drive as...
1,870