I'm trying to build a cable to connect twido plc (RS485) and altivar71 (RJ45). Anyone knows pin-out for this connection? Does it matter which ethernet cable i use (a or b, images attached)? Thanks!
It should be a fairly easy connection. It doesn't matter which type of Ethernet cable you use since the RJ-45 connector doesn't actually use Ethernet at all, and you only need positions 4 and 5 which are the same colors on both types. You'll connect the blue and blue/white pair to terminals A and B on the Twido. You'll have to try both polarities to determine which is correct.
So i don't need to use the third pin (SG) on rs485 connector? I will try that, thank you very much! :)
If you have any issues, connect the brown wire from the Ethernet cable to SG.
Thank you, i've made the cable but i'm still unable to start the motor. I use following devices:
HMI XBTGT 4330 7"
Programming software: VijeoDesigner 4.6.0.7613
Twido PLC TWDLCAE40DRF
Programming software: TwidoSuite 2.0
Altivar 71
Ethernet communication between HMI and PLC works fine, i can set the speed on HMI and correct value is displayed in animation table on PLC. I used following settings on Altivar:
Communication - Modbus Network:
Address: 2
Baudrate: 19200
Data bits: 8
Time between frames: 10
Command: Ref.channel 1: Modbus
Ch1 active
Profile Not separ.
System word %SW64 keeps returning (modbus) error code 8. I have NST message on Altivar with these settings; if I try to use I/O profile it says RDY but does not receive anything from PLC, or returns CRC 2. I've read manuals, checked wiring and tried pretty much everything I could think of, but no luck :(
HMI and Twido programs are included in attachment. I would be very grateful for any suggestion regarding this issue. Tyvm!
Looking over your Twido program I have noticed that both RS485 ports (mini-din) and the terminal block option block share the same Modbus address of 1.
Hello guys, I am trying to control a ATV12 via Modbus Poll software. I need the connection diagram for Altivar Modbus RJ45 port to DB9 port. Thank you
582
What is a good method to daisy-chain a number of RS485 4-wire devices that only have RJ45 ports. Is there a special device or adapter or do you...
1,841
What do you guys use for connecting several Modbus RS485 devices with a single RJ45 port in the one panel? and terminating resistors?
3,070
I'm connecting up two remote ethernet devices to the switch in my control panel, and I'm trying to do the cleanest install. The customer typically...
603
Hi, I have a SLC5/03 connected to a working HMI via RE232 port, and connected to a broken HMI via DH485 (RJ45), I want to use the cable that used...
3,338