Totalizer Not Couting

Dera bsee

Member
Join Date
Sep 2012
Location
Los Angeles
Posts
36
Hi all,

I'm using a totalizer for the first time and it's not counting. I have the ProgStartReq set and nothing. I am calling the routine.

I attached how I configured the instruction. Thanks all :site:

totalizer_config_1.jpg totalizer_config_2.jpg
 
Your totalizer is under operator control.
You need to raise ProgProgReq to switch it to program control.

(Look to the status of ProgOper)
 

Similar Topics

Hi, So we have a flowmeter installed but doesnt have a feature to send a pulse to plc for it to compute the total volume. I want to somehow...
Replies
3
Views
574
How is it going y'all? So We have had a pesky problem with an EH 300 flow meter. We are using EIP to reset the totalizer, and for some reason the...
Replies
3
Views
789
Good morning, I have a flow meter that has an output pulse configured to 378.541 liters per pulse. My question is, do I just count the pulse per...
Replies
19
Views
1,802
Good morning, I have a flow meter that that has an output with is a pulse. The pulse is configured to 378.541 liters per pulse. My question is...
Replies
6
Views
701
Hello You guys helped me with a similar issue some time back on storing totalized values to different tags each month. I have a similar issue...
Replies
19
Views
1,492
Back
Top Bottom