Help required For Guard Logix CPU L71S

We are facing following problems for gurad logix

1) How we can edit the safety Program and safety tags

2)Could not change the Safety Modules Properties

Is there is any procedure for that or it is software end Problem using Studio 5000 standard edtition

After that we send Empty program with Existing Hard ware then At online it gives I/O Not OK communication not established bw EN2tr to AENTR and its safety point ios
 
You have to unlock the safety to change anything safety related....in the upper left of logix while online does it show locked or unlocked?
 
You can't modify any safety programs using Logix Standard Edition. You will need Full or Professional edition.

And, as robertmee said, you'll have to have the safety unlock password too.
 

Similar Topics

Hello, I'm adding an Allen-Bradley SensaGuard door switch (440N-Z21SS2H) to a small existing machine to drop out pneumatic function when the...
Replies
3
Views
987
Hi to the forum. I have a logic problem which is confusing me. From my sketch I have seven conveyors that I control using a twido PLC via canbus...
Replies
19
Views
5,614
Hi guys, I need help with position control using a Veichi AC Servo Drive model SD600A1-T2-2R2. How do I know how many pulses for it to rotary 1...
Replies
0
Views
12
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
Replies
0
Views
36
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
9
Views
298
Back
Top Bottom