Omron PLC CPU Not Writing Configuration to ETN21
scrambled
Jul 2015
Brisbane
108
Hi all,
We've encountered a bit of a puzzling issue with an Omron CJ1M-CPU12 PLC on a site. Basically, it's not letting us write configuration changes to the ETN21 card on the rack.
All we want to do is change in the ETN21 is the IP address/subnet mask and add an IP address conversion entry. However, when we download the entire modified PLC program, the ladder code changes are updated but when we read the ETN21 configuration, it is unchanged.
When we try to transfer the ETN21 parameters separately with the 'Transfer[PC to Unit]' option, we get an error message that reads "Mode 11 - cannot download". I haven't been able to find any information on what this message means.
We have tried several spares of ETN21 cards, with different firmware versions (1.4 and 1.5) and we still encounter the same issue. This leads us to believe it is something to do with the Omron CPU. For whatever reason, it is not letting us modify the configuration of the Bus units.
Another thing is there is an identical Omron PLC on another site that has practically the same program and same rack and unit configuration. We were able to download those same program changes to that PLC last week with no issue at all. This makes me suspect some sort of hardware fault as the root of our woes.
Do any Omron experts hear have any idea what could be the possible causes of our issue?
Thanks for the info.
The customer had a spare CJ1M CPU unit, so we managed to resolve the issue by replacing the running CPU with the spare. Our guess is that the old CPU had some sort of flash memory issue where it wasn't able to write Unit configuration changes.
Just came across this post while trying to resolve the same issue.
The simple solution is to flip the ETN21 to ETN11 mode;
PLCIO Table, Highlight the ETN module and select Options, Change ETN mode.
This will flip the ETN mode from 21 to 11 (or 11 to 21 depending on your initial setting).
Then repeat the above to flip the ETN back to the desired mode and you should be able to download the settings.
Don't know why this works - I suspect its resetting something in the memory (?) 🍻
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
214
Hi I have a plc omron CJ1M connected to a HMI this is a reconditioned panel in which this plc is connected. But the touch screen of the HMI is not...
3,582
hello sir .. i have queestion to ask ..regarding omron plc units ,, recently .i wanted to connect omron PLC unit (c200he to HMI) which locate...
2,965
Dear Friends, can you help me to extract the ladder diagram from protected omron cpu unit model (CQM2H), i know that their are some way to open...
1,895
Hi All Iam using plc omron (sysmac cqm1 cpu 11), i have a problem on out put module (oc222)and want to replace the module, my problem that...
7,013