Studio 5000 RIO Module Help

Join Date
May 2017
Location
Regina
Posts
12
Hello I am trying to do some testing on the bench. I have a 1756-L73 processor, 1756-RIO and a plc5 rack with a RIO module. I have set up my 5000 program and am trying to use the configuration tool for the rio module. However after making my .rio file and i goto Tools>Set 1756-RIO Module Scanner/Adapter Mode I get the following error:

"DTL_E_MISSING_RSLINX_ACTIVATION, unable to find activation key"

Any ideas?
 
From Rockwell............

Per the ControlLogix Remote I/O Communication Module User manual, Publication 1756-UM534 and ControlLogix Remote I/O (RIO) Module Installation instructions, Publication 1756-IN610, the 1756-RIO module requires RSLinx Classic v2.54 or greater and RSLinx Classic must have an activation
 

Similar Topics

We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
Replies
1
Views
414
Recently we've had some faults and disconnects with our 1734 aent/r module. It shuts down all processes associated with the remote IO, obviously...
Replies
8
Views
3,347
Hi, how do I convert 2x Integer registers to a Real? The two integers are from Modbus registers that contain a floating point value, I need to...
Replies
2
Views
103
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
Replies
3
Views
101
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
Replies
0
Views
64
Back
Top Bottom