ScanPro to Powerflex 70

Join Date
Oct 2007
Location
TN
Posts
2
Does anyone know what parameters I have to set in a Powerflex 70
so that the scanport card can control it. This is an upgrade so
the PLC programming is in place, but the Powerflex 70 is an upgrade. Thanks, Any info will be helpful.
 
I believe that you have set set your start/stop source and speed source to DPI port 2

par 90 Ref Sel A - DPI port 2
par 361 Dig In 1 - 0
par 362 Dig In 2 - 0
 