Money4Nothing
Member
I have a Panelview Plus and Compact Logix L32E processor connected with a laptop via an ethernet switch. Actually, I'm on the phone with a tech in the field trying to load the project.
The proc and Logix5k are version 13, and they are running RSView studio ME 4.0 on the laptop. When they run the test feature on Studio all the tags and variables from the PLC operate fine. But when they compile and load the runtime .mer into the Panelview, there is no tag communication.
We can see both devices on RSLinx, and they're online with everything from the laptop. They can transfer the project to the terminal from RSView no problem. But somehow the PV+ isn't seeing the tag server on the proc. I'm baffled, becuase we can test the same project on the RSView studio test runtime, and it works fine.
All my firmware checks out with my software versions, unless there is some minor incompatibilities that I'm unaware of.
I've never come across this before...any ideas on what to check next?
Thanks in advance.
$
The proc and Logix5k are version 13, and they are running RSView studio ME 4.0 on the laptop. When they run the test feature on Studio all the tags and variables from the PLC operate fine. But when they compile and load the runtime .mer into the Panelview, there is no tag communication.
We can see both devices on RSLinx, and they're online with everything from the laptop. They can transfer the project to the terminal from RSView no problem. But somehow the PV+ isn't seeing the tag server on the proc. I'm baffled, becuase we can test the same project on the RSView studio test runtime, and it works fine.
All my firmware checks out with my software versions, unless there is some minor incompatibilities that I'm unaware of.
I've never come across this before...any ideas on what to check next?
Thanks in advance.
$