HMI Communication
Before you posted your question, did you try a search 'weintek siemens mpi' with google? Weintek has a PLC Connection Guide Document that seems to explain everything you may need.
Dear nwboson,
I know how to connect single Weintek HMI with single MPI port. But my question is How to connect two HMI with single MPI port/
Regards,
If you perform the google search I mentioned earlier, you will find the Weintek document 'Siemens_S7_300_MPI.pdf'.
It explains you will set the station number of the first HMI to zero and the station number of the second HMI to one (this is under System Parameter Settings->Model tab in EasyBuilder Pro). You will set the maximum station number to 2 (in the MP300 driver Settings of EBPro) and the PLC at station 2 (in the Siemens PLC software).
There are also limitations about which model numbers of HMI are capable of multiple HMI, multiple PLC: please refer to that document above.
As far as wiring, it is simple 2 wire RS485: daisy chain all three devices and terminate at the ends appropriately. If you need more information regarding daisy chaining RS485, there is a wealth of information available through google searches.
Hope that helps...
Not sure if this is even possible but I have an micro 1400 that I would like to connect to HMI. I am using rs232 from PLC to (RS232/ttl converter)...
226
Hello everyone, I am trying to change the IP address of the Omron PLC (NJ30-1200) and HMI (NB7W-TW01B) to fetch the network on our network...
286
hi everyone. i hope you guys are doing great. i am trying to built communication between aveva intouch hmi 2023 and tia portal v18. i dont have...
566
Hello, I'm facing a problem in communication between my delta TP70P-32TP1R HMI and DVP20EX2 PLC. I tried multiple ways in order to set the...
1,333
Story time: We have two similar machines on a Factorytalk View Distributed Network. This SE server has several different machines on it as well...
572