VFD control throw profibus S7 TIA V13

I have VFD Schenider ATV 61. I would like to know how I can control it throw profibus. Dp V0 .. Siemens TIA V 13 .

If you get the GSD file from Schneider, then you can import the drive into Portal. That allows you to add it in Portal, assign it to IO addresses in the PLC, etc.

However, you'd also need documentation on the telegrams, ie what each of the bits and bytes mean. There may be FB's developed to help you with that, but you may also have to sort it yourself, based on the drive manual.
 
What is the problem you are running into?

I am not familiar with this VFD, but generally speaking you would be sending two words to the drive. One control word (start/stop, direction etc) and one speed.

This is assuming you set up the drive correctly.

First google result brings up this manual, it is for DPv1, but should help you.
 

Similar Topics

Hello, I’m new to this forum and if I’m posting incorrectly let me know. I’ve been having an issue I can’t seem to figure out. I’m sure it’s...
Replies
1
Views
119
Hi there, We have a system at a water treatment plant where large raw water tanks feed into the plant that's all on the same level. At high tank...
Replies
18
Views
3,763
Hello, So I was asked to turn up the speed on a VFD to allow a carriage to move a little bit faster and avoid getting stuck. Im not sure the exact...
Replies
2
Views
736
Hello everyone, I have yet another thread about PID's coming your way. Any PLC5 users in the house? I'm currently writing a program and have...
Replies
6
Views
2,128
I am controlling a very tight window in a 8 foot sump. My low level to keep from cavitating the pump is 44” and my high level is 55”. The problem...
Replies
9
Views
2,070
Back
Top Bottom