Hi Guys,
I have a fault with a 1769-OF8V that has been in service now for over two years. The data is going to the outputs on the module when I'm monitoring live from the plc but there is no change in voltage output and no active fault alarms on the plc. When I do a power reset on the system the outputs start to work again for a few days. The outputs are driving the analogue inputs for speed control on WEG CFW700 VSD's.
Has anyone had this issue before? I'm inclined to say the module is faulty and needs replaced but without a complete failure of the component it's a difficult one to call. I can't understand how a power reset gets the module up and running again if it was faulty. Surely this would imply a software issue.
Anyone any ideas?
I have a fault with a 1769-OF8V that has been in service now for over two years. The data is going to the outputs on the module when I'm monitoring live from the plc but there is no change in voltage output and no active fault alarms on the plc. When I do a power reset on the system the outputs start to work again for a few days. The outputs are driving the analogue inputs for speed control on WEG CFW700 VSD's.
Has anyone had this issue before? I'm inclined to say the module is faulty and needs replaced but without a complete failure of the component it's a difficult one to call. I can't understand how a power reset gets the module up and running again if it was faulty. Surely this would imply a software issue.