I'm trying to setup a Profibus link between a CTI 2500-C200 PLC and a MTL 8507-BI-DP. I'm using FasTrack 505 Workshop V5.10.
I've tried a few different versions of the .GSD files from MTL as well as a newer one from GE who were looking after this product after MTL.
The configuration loads ok into the PLC, but the 8705 slave module always shows "Status: Offline" in the Profibus I/O configuration window.
STW231.1 is on (DP Operate)
STW231.6 is on (Slave Error)
All other bits of STW231 are off
The 8705 Slave Diagnostics window changes values when I connect/disconnect the profibus cable - so I know it's communicating.
With cable connected the diagnostics show:
"Slave not ready for data exchange = Yes"
"Incorrect parameterization = Yes"
"Slave has to be parameterized = Yes"
"Watchdog activated = Yes"
When I unplug the cable these all change to "No"
Has anyone had any success with configuring the MTL 8507 BIM?
regards, Phil
Hello Phil, let's start from the beginning. Are you using standard Profibus media, and is there correct termination at both sides of the Profibus segment. How long is the overall cable length and what baud rate has the master been setup. Did you try a slower baud rate?
Sounds to me as
either the Profibus master is not connected at all,
or the configuration of the modules in the MTL rack as setup in the CTI CPU does not match the real rack setup.
Does the CTI PLC have other Profibus slaves, and if so does the communication with these work OK ?
Hi All, got an issue with a PLC5 Profibus adapter card and it looks as though I need some legacy software (Local Station Manager) to configure the...
754
Hi everyone, I'm trying to learn how to make hardware configuration. I have an IM on profibus. I added the whole group (I dragged the marked taxed...
1,180
Maybe there is some easy solution, but I can't figure out how it should be done.. Actually, I don't even know how I can clearly explain what I...
1,690
Hi there! I am trying to connect my SST Profibus in our Controller using RSLinx Classic. When I right-clicked my Master SST and then go to the...
2,683
I am relatively new to profibus, and thus not fully aware of its capabilities. Do the devices as configured in prosoft need to be connected in...
1,956