UNI 4401 VFD Problem
Hi everybody how are you today?
I have problem with UNI4401 VFD. Once I turned On 480VAC input power to L1-L2-L3, there is unbalance output voltage on U-V-W instantly, even all feedback wire are unplugged. What is the possibility problem ? I need somebody help me out. Also could I get complete schematic diagram for this AC Drive? I am really appreciate to your time and attention. Best Regard, Benyamin |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 506
|
Dumb question, but is the input power balanced? Check all 3 phase-phase and phase-neutral. The manual should provide a range of acceptable values. If that's good, then there's probably something wrong with the drive.
I seriously doubt you'll find detailed schematics of the insides of any drive. |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Jan 2021
Location: Asheboro, NC
Posts: 2
|
Input doesn't equal output
With AC drives, the three phase input power is rectified to DC and store in BUS capacitors. The plus and minus of these capacitors feed to six IGBT's which through the circuitry develops a three phase PWM output to the output of the drive. If any of the IGBT's or the driving circuitry is bad, you will get an imbalance on the output. The drive needs to sent in for repair.
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 280
|
I'm not familiar with this particular drive, but is there an Autotune routine available?
|
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
Hello Joseph_e2,
Yes, three phase input voltage are equal (480V). With solid neutral connected to the right terminal. There is no schematic diagram inside drive. Anyway I appreciate to the response. I am still expecting others to help me. Thank you Benyamin |
![]() |
![]() |
#6 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 290
|
There isn't really any reason for a VFD to put different voltages on the wires going to the motor. All the output phases should be equal within the drives specifications (+- a few percent), any other condition is almost certainly a cause for repair or replacement of the drive.
joseph and wildbill both presented this solution earlier. |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
Dear Friends,
Thank you for all responses regarding to my issue. I agree with Wildbill9669's idea. I will TEST those 6 IGBTs, if there is bad one I will replace it Monday. But the next question is why there is voltage on output side, even there is no any feedback as I mentioned on my first email, also no voltage reference yet. In other word is why those IGBTs turned on without any reference signal? Any ideas are wellcome. Thank you. Benyamin |
![]() |
![]() |
#8 |
Member
|
Do you have a motor connected to this drive?
Keith |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
Yes I do
|
![]() |
![]() |
#10 |
Member
|
What level of voltage are you seeing? Single digit volts, tens of volts or hundreds of volts? Is the motor moving at all?
Keith |
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
125-90-130
|
![]() |
![]() |
#12 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
The motor was moving but noisy and run internittrn/jogging
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
Sorry wrong typing. It is running intermitten
|
![]() |
![]() |
#14 | |
Member
![]() ![]() Join Date: Mar 2012
Location: Dallas
Posts: 66
|
Quote:
I found 1 bad IGBT and replaced it. But the symptom is still same. I think control board has problem. Would you tell me where are the signals for all IGBTs come from? From controlboard or module placed in the keypad area? Anybody please response to my issue please. I appreciate to your attention. Thank you, Benyamin |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Delta PLC to LS VFD Modbus problem | Mufti | LIVE PLC Questions And Answers | 8 | July 22nd, 2021 12:16 PM |
SLC 5/04 and VFD problem.....need help | JoseM | LIVE PLC Questions And Answers | 6 | March 2nd, 2012 04:45 PM |
OT: Headscratcher problem with servo hydraulic cylinder. | TConnolly | LIVE PLC Questions And Answers | 12 | October 9th, 2008 08:59 PM |
Ab Plc5 Rio Problem. | fernandes | LIVE PLC Questions And Answers | 5 | March 7th, 2004 02:25 PM |
PLC5/40 Backplane Problem????? | Andrew Evenson | LIVE PLC Questions And Answers | 18 | August 24th, 2002 08:06 PM |