UNI 4401 VFD Problem

Hi everybody how are you today?
I have problem with UNI4401 VFD.
Once I turned On 480VAC input power to L1-L2-L3, there is unbalance output voltage on U-V-W instantly, even all feedback wire are unplugged. What is the possibility problem ? I need somebody help me out.
Also could I get complete schematic diagram for this AC Drive?
I am really appreciate to your time and attention.

Best Regard,
Benyamin
  Reply With Quote
Old March 17th, 2023, 01:48 PM   #2
joseph_e2
Member
United States

joseph_e2 is offline
 
Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 506
Dumb question, but is the input power balanced? Check all 3 phase-phase and phase-neutral. The manual should provide a range of acceptable values. If that's good, then there's probably something wrong with the drive.

I seriously doubt you'll find detailed schematics of the insides of any drive.
  Reply With Quote
Old March 17th, 2023, 02:12 PM   #3
wildbill9669
Member
United States

wildbill9669 is offline
 
Join Date: Jan 2021
Location: Asheboro, NC
Posts: 2
Input doesn't equal output

With AC drives, the three phase input power is rectified to DC and store in BUS capacitors. The plus and minus of these capacitors feed to six IGBT's which through the circuitry develops a three phase PWM output to the output of the drive. If any of the IGBT's or the driving circuitry is bad, you will get an imbalance on the output. The drive needs to sent in for repair.
  Reply With Quote
Old March 17th, 2023, 02:23 PM   #4
jaden
Member
United States

jaden is offline
 
Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 280
I'm not familiar with this particular drive, but is there an Autotune routine available?
  Reply With Quote
Old March 17th, 2023, 04:03 PM   #5
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
Hello Joseph_e2,
Yes, three phase input voltage are equal (480V). With solid neutral connected to the right terminal.
There is no schematic diagram inside drive. Anyway I appreciate to the response.
I am still expecting others to help me. Thank you

Benyamin
  Reply With Quote
Old March 17th, 2023, 04:15 PM   #6
Robb B
Lifetime Supporting Member
Canada

Robb B is offline
 
Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 290
There isn't really any reason for a VFD to put different voltages on the wires going to the motor. All the output phases should be equal within the drives specifications (+- a few percent), any other condition is almost certainly a cause for repair or replacement of the drive.

joseph and wildbill both presented this solution earlier.
  Reply With Quote
Old March 17th, 2023, 07:24 PM   #7
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
Dear Friends,
Thank you for all responses regarding to my issue.
I agree with Wildbill9669's idea. I will TEST those 6 IGBTs, if there is bad one I will replace it Monday. But the next question is why there is voltage on output side, even there is no any feedback as I mentioned on my first email, also no voltage reference yet.
In other word is why those IGBTs turned on without any reference signal?
Any ideas are wellcome.

Thank you.
Benyamin
  Reply With Quote
Old March 17th, 2023, 07:30 PM   #8
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,276
Do you have a motor connected to this drive?

Keith
  Reply With Quote
Old March 17th, 2023, 07:32 PM   #9
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
Yes I do
  Reply With Quote
Old March 17th, 2023, 07:33 PM   #10
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,276
What level of voltage are you seeing? Single digit volts, tens of volts or hundreds of volts? Is the motor moving at all?

Keith
  Reply With Quote
Old March 17th, 2023, 07:35 PM   #11
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
125-90-130
  Reply With Quote
Old March 17th, 2023, 07:38 PM   #12
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
The motor was moving but noisy and run internittrn/jogging
  Reply With Quote
Old March 17th, 2023, 07:41 PM   #13
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
Sorry wrong typing. It is running intermitten
  Reply With Quote
Old March 24th, 2023, 03:06 PM   #14
Benyamin
Member
United States

Benyamin is offline
 
Join Date: Mar 2012
Location: Dallas
Posts: 66
Quote:
Originally Posted by wildbill9669 View Post
With AC drives, the three phase input power is rectified to DC and store in BUS capacitors. The plus and minus of these capacitors feed to six IGBT's which through the circuitry develops a three phase PWM output to the output of the drive. If any of the IGBT's or the driving circuitry is bad, you will get an imbalance on the output. The drive needs to sent in for repair.
Hello Wildbill9669,
I found 1 bad IGBT and replaced it. But the symptom is still same.
I think control board has problem. Would you tell me where are the signals for all IGBTs come from? From controlboard or module placed in the keypad area?
Anybody please response to my issue please.
I appreciate to your attention.

Thank you,
Benyamin
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Delta PLC to LS VFD Modbus problem Mufti LIVE PLC Questions And Answers 8 July 22nd, 2021 12:16 PM
SLC 5/04 and VFD problem.....need help JoseM LIVE PLC Questions And Answers 6 March 2nd, 2012 04:45 PM
OT: Headscratcher problem with servo hydraulic cylinder. TConnolly LIVE PLC Questions And Answers 12 October 9th, 2008 08:59 PM
Ab Plc5 Rio Problem. fernandes LIVE PLC Questions And Answers 5 March 7th, 2004 02:25 PM
PLC5/40 Backplane Problem????? Andrew Evenson LIVE PLC Questions And Answers 18 August 24th, 2002 08:06 PM


All times are GMT -4. The time now is 06:25 AM.


.