Hi Folks,

I am planning to use 1783-NATR with my packing machine. Machine has Rexroth PLC(IndraControl L40) with IP 169.204.201.100. I am suppose to fetch this PLC's data over OPC but unfortunately, I can not connect the same to my OT network with existing IP. So i need to translate this IP to 172.30.210.X

Does NATR work with any PLC's IP translation? :unsure:

Regards,
Mihir
 
You should be able to map 32 ip addresses on your private network to new addresses on the public 172.20.210.x network. You will need to set the NATR as the default gateway of your private network so that traffic can get out of the private network.

It is just a NAT router and should work on any tcp/ip device. It has some special sauce to allow it to be configured via ethernet ip but is isnt needed.
 

Similar Topics

Is it possible to gather OPC data through a 1783-NATR? Searching around, it sounds like OPC data might be blocked by any NAT... Is there any work...
Replies
2
Views
246
Good morning all, I have a project that has quite a few NATRs to configure. I would like to modify the generated backup config file because I...
Replies
2
Views
432
I am trying to communicating with other PLCs on a public network from a CompactLogix PLC on a private network. I have installed at 1783-NATR...
Replies
1
Views
556
Hello, I'm seeing some interesting behavior with my NATR connections on FTLinx. 2 separate cases are showing the same problem: The first NATR...
Replies
0
Views
622
Hello, I have been trying to set up a NATR with 3 connections, I am able to ping the public IP of the NATR itself off of my network, but nothing...
Replies
3
Views
679
Back
Top Bottom