Old May 16th, 2018, 04:41 PM   #1
lesmar96
Lifetime Supporting Member
United States

lesmar96 is online now
 
Join Date: May 2017
Location: PA
Posts: 216
overvoltage fault on vfd

I am having some issue with two vfds installed at the same location. They are tripping out on overvoltage faults very randomly. I checked the incoming voltage, and at 245, it is pretty high, but not high enough to get the utility company to look at it.

The one drive is running a bandsaw. We have plenty of decel time programmed in. It seems it faults out when the the load changes very rapidly. Like it tends to trip out, right when they hit a knot in the log etc. It is a bit puzzling to me why rapid fluctuation on the load would create an overvoltage condition. The only thing I can think of is if the motor is somehow creating a regen when the load suddenly lessens. But I wasn't sure what to change in the programming to get around it.

I would appreciate any thoughts you would have on this.
  Reply With Quote
Old May 16th, 2018, 04:52 PM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,204
Please post the brand and model of the vfd units so we can better assist you.

james
  Reply With Quote
Old May 16th, 2018, 04:53 PM   #3
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,550
Common cause:
1) Regeneration takes place when you have the motor energized (excited), AND the output frequency is lower than the load speed. Lengthening the decel time can help dampen a rapid change in speed to help the load dissipate more of it's kinetic energy via friction and other load losses, but it is not a "cure".

2) If you have the VFD set to current limit rather than trip on a high change in load, you can get yourself in trouble. What a VFD will do to limit the current is to override your commanded speed and lower the output frequency in an attempt to shed load on the motor. This also overrides your decel time so if the change in load is too fast, the rapid drop in output frequency becomes an issue allowing for regen as described above.

One thing to consider: why do you have decel enabled at all on a band saw? Decel is used to PREVENT a load from stopping faster than it would naturally, for example a pump to avoid creating water hammer. I see no benefit in having decel enabled on a band saw. Just turn it off. Usually you do that by setting the "Stop mode" to "Coast". If you want to stop the band saw FASTER than it will coast, then you want BRAKING, not decel. Decel is the OPPOSITE of braking.
  Reply With Quote
Old May 16th, 2018, 05:49 PM   #4
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,645
Quote:
Originally Posted by jraef View Post
Decel is used to PREVENT a load from stopping faster than it would naturally...Decel is the OPPOSITE of braking.
I've never thought about it in that depth. I've learned my new thing for the day!
  Reply With Quote
Old May 17th, 2018, 05:26 AM   #5
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 265
Quote:
The only thing I can think of is if the motor is somehow creating a regen when the load suddenly lessens. But I wasn't sure what to change in the programming to get around it.
I've seen this many times. Basically it comes down to either a poor tuning, or just the load dynamics being too much for the drive to handle without some persuasion.
Most medium to high performance drives have current limits for both motoring and braking/regenerating. By limiting the braking torque through current limit, the drive can ignore some of the regenerated energy an use it later.
The alternative is to waste the energy into a shunt/DB resistor to regulate the speed.

It just depends on what hardware you have, how precise speed regulation is, and how much you want to spend.
  Reply With Quote
Old May 17th, 2018, 05:41 AM   #6
bitmonkey
Lifetime Supporting Member
United States

bitmonkey is offline
 
Join Date: Oct 2015
Location: Ohio
Posts: 75
Check your mains voltage. I once had an overvoltage fault because the AC supply voltage was too high.
__________________
I want to die peacefully in my sleep, like my grandfather, not screaming in terror like his passengers.
  Reply With Quote
Old May 17th, 2018, 06:02 AM   #7
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 22
Overvoltage faults can be caused by a few things. The most common is minor, quick fluctuations in the incoming power to your drive. At the plant I work at, we have fluctuations all the time. The power supplied is within the power company's specifications, but on the high side of the specification. That means that any increase in voltage could put us over the drive's incoming voltage spec. We have eliminated the problem by installing line reactors on the incoming power leads to the drives. Reactors do a great job of smoothing those fluctuations.
Another is regeneration, as mention previously. This is not likely the case on a band saw if it is happening during a cut.
Third, poor grounding of the motor and drive can cause the drive to believe it is in a regenerative mode and cause trips.
  Reply With Quote
Old May 17th, 2018, 06:49 AM   #8
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is online now
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,328
In this case it is not because of trying to stop too fast or because of incoming supply voltage fluctuations.
Quote:
The one drive is running a bandsaw. We have plenty of decel time programmed in. It seems it faults out when the the load changes very rapidly. Like it tends to trip out, right when they hit a knot in the log etc.
The problem is when some of the masses in the machine changes from being driven by the drive, to sending energy back to the drive, you get the overvoltage.

The remedy is to use a brake chopper (sonetimes integrated into the drive) and a brake resistor (usually an option that has to be installed outside the drive).
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 17th, 2018, 06:55 AM   #9
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is online now
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,328
Quote:
Originally Posted by drforsythe View Post
Another is regeneration, as mention previously. This is not likely the case on a band saw if it is happening during a cut.
Why not ? I imagine that of passing a knot and there may be some kind of mechanical slack, you can get the effect that the mechanism oscillates in a way that changes from being driven to regenerating.
If he says that it happens when the load changes, then that is an indicator that it has to do with the load.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old May 17th, 2018, 07:16 AM   #10
lesmar96
Lifetime Supporting Member
United States

lesmar96 is online now
 
Join Date: May 2017
Location: PA
Posts: 216
Quote:
Originally Posted by jraef View Post

One thing to consider: why do you have decel enabled at all on a band saw? Decel is used to PREVENT a load from stopping faster than it would naturally, for example a pump to avoid creating water hammer. I see no benefit in having decel enabled on a band saw. Just turn it off. Usually you do that by setting the "Stop mode" to "Coast". If you want to stop the band saw FASTER than it will coast, then you want BRAKING, not decel. Decel is the OPPOSITE of braking.
The drive defaults at 20 seconds decel and that is where I left it. I have not set it to coast to stop. I do have the DC injection breaking turned on so that it does not coast so long for safety.

I thank you all for your replies. Sounds like a resistor might be the best solution? It is a Fuji Electric, Mega series. I will have to check about the current limiting.
  Reply With Quote
Old May 17th, 2018, 07:17 AM   #11
lesmar96
Lifetime Supporting Member
United States

lesmar96 is online now
 
Join Date: May 2017
Location: PA
Posts: 216
Quote:
Originally Posted by drforsythe View Post
Third, poor grounding of the motor and drive can cause the drive to believe it is in a regenerative mode and cause trips.
Can you please explain this comment a bit more? I'm quite certain grounding is not a problem. Just wondering about the logic behind this.
  Reply With Quote
Old May 17th, 2018, 07:20 AM   #12
lesmar96
Lifetime Supporting Member
United States

lesmar96 is online now
 
Join Date: May 2017
Location: PA
Posts: 216
This regen voltage problem is only made alot worse by our high incoming voltage? The drive trips out at 400V on the DC bus. In the trip history, it registered at 406VDC when it tripped.
  Reply With Quote
Old May 17th, 2018, 07:52 AM   #13
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 22
I used to see this a lot when I worked for a company that supported one of the Japanese drive manufacturers. The circuitry that would monitor for regenerative overvoltages was really sensitive. When grounding was the issue it would trip even when the motor shaft was sitting still and there was no commanded motion (and therefore no chance of regen). It seemed to occur mostly on older machine retrofits where the original wiring was questionable or on monorail drives where the drive ground came through a brush system. The manual for the drive even mentioned to check motor and drive grounding when that error occurred.
  Reply With Quote
Old May 17th, 2018, 11:51 AM   #14
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 265
Quote:
Originally Posted by lesmar96 View Post
Can you please explain this comment a bit more? I'm quite certain grounding is not a problem. Just wondering about the logic behind this.
Most drives have some form of input line filtering, from very basic to pretty substantial. When you don't have a good ground, the capacitance of the filtering can charge up to a point that it will cause a high voltage trip on the DC bus. Normally, the caps would shunt the high frequency noise to ground.
  Reply With Quote
Old May 17th, 2018, 01:57 PM   #15
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,550
Is it a 240V 3 phase delta supply then? If so, and it is an ungrounded delta or one phase is center tapped (high leg delta), many Asian drive designs have trouble with delta power systems, because are expecting the supply to be referenced to ground, which is not if it's delta. Then as Gene Bond explained, that can lead to the common mode noise having nowhere to go and building up on the DC bus.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
TwinCat and Indramat F268 Brake Fault boldive LIVE PLC Questions And Answers 0 December 4th, 2008 09:55 AM
AB 160 VFD Clear Fault Buffer? OkiePC LIVE PLC Questions And Answers 2 November 30th, 2008 12:39 PM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 02:55 PM
VFD -- Reverse only one of two motors leitmotif LIVE PLC Questions And Answers 7 September 25th, 2007 12:41 PM
VFD generates overvoltage alarm at startup. JesperMP LIVE PLC Questions And Answers 16 August 19th, 2004 07:23 PM


All times are GMT -5. The time now is 02:05 PM.


.