Step 7 OBs for redundancy error

Hi All,
I have a S7-400 H redundant system & have included following OBs mentioned in the manual that are required for redundancy -
OB 70,72,80,82,85,86,87,88,121,122.
Do I have to write any more program to activate these OBs or by just including them they start working?
Manual mentions that the OBs are necessary as they prevent CPU from going into stop mode on error. If this correct?
I would like to build a small diagnostic to know what error is causing the SF LED to be lit.

Any suggestions?

Thanks,
  Reply With Quote
Old January 24th, 2007, 11:59 AM   #2
PeterW
Member
Canada

PeterW is offline
 
Join Date: Jun 2006
Location: Edmonton
Posts: 2,522
The OB's will be empty and just leaving them that way will stop the PLC from going into stop on error, bare in mind tht depending on the process this could be dangerous.

Look at the help on each OB, the TEMP flags in the header is where all the information on the cause is stored and you may want to not just record the reason but determine whether or not its safer to stop the PLC, which you can only do by calling the STOP SFC46.
  Reply With Quote
Old January 25th, 2007, 01:43 AM   #3
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Thanks Peter,
I will give it a try.
  Reply With Quote
Old January 25th, 2007, 11:21 PM   #4
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Quote:
Originally Posted by PeterW
The OB's will be empty and just leaving them that way will stop the PLC from going into stop on error, bare in mind tht depending on the process this could be dangerous.

Look at the help on each OB, the TEMP flags in the header is where all the information on the cause is stored and you may want to not just record the reason but determine whether or not its safer to stop the PLC, which you can only do by calling the STOP SFC46.
I would like to know how do I reset the flags built in the ladder which resides in OB 70? My understanding is that the CPU call OB 70 only on error; rest of the time it is not executed.
I have written a simple ladder in OB 70 which identifies the Failed DP master address & ID. Do i need to put an external reset flag after the operator has seen the fault?
Any suggestions?
  Reply With Quote
Old January 26th, 2007, 02:16 AM   #5
PeterW
Member
Canada

PeterW is offline
 
Join Date: Jun 2006
Location: Edmonton
Posts: 2,522
Would you want the operator to reset the alarm an continue regardless??

To answer the question though, the OB is only called on fault so the reset of any faults would have to be done externally.
  Reply With Quote
Old January 26th, 2007, 04:00 AM   #6
Ken M
Member
Scotland

Ken M is offline
 
Join Date: Mar 2004
Location: .
Posts: 1,136
I can't remember if this applies specifically to OB70, but for many of the fault OBs they are called twice: once when a fault arises, and once when a fault clears. There is a TEMP variable that identifies whether each run is in response to entering or leaving a fault state.

[... brief passage of time ... ]

OK, I've just done what I should have done before starting to write this. I checked the manual!

The TEMP variable is OB70_EV_CLASS (event class) and this will hold one of two values on each execution. It's a byte-length variable and a value of B#16#72 means an outgoing event (clear) and B#16#73 means incoming event (fault).
So you can write your fault-handling and resetting code in the same OB and just select according to the value of OB70_EV_CLASS. Remember also that you don't have to put all your code directly in OB70 itself. It can call FCs, FBs as well just like OB1. You can have a very structured response to abnormalities based on checking EV_CLASS, FAULT_ID etc.

Regards

Ken
  Reply With Quote
Old January 26th, 2007, 09:21 AM   #7
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Quote:
Originally Posted by Ken M


The TEMP variable is OB70_EV_CLASS (event class) and this will hold one of two values on each execution. It's a byte-length variable and a value of B#16#72 means an outgoing event (clear) and B#16#73 means incoming event (fault).
So you can write your fault-handling and resetting code in the same OB and just select according to the value of OB70_EV_CLASS. Remember also that you don't have to put all your code directly in OB70 itself. It can call FCs, FBs as well just like OB1. You can have a very structured response to abnormalities based on checking EV_CLASS, FAULT_ID etc.

Regards

Ken
Ken Thanks. I never looked deeply into the meanings of outgoing & incoming events . Your reply realy helps.
  Reply With Quote
Old January 27th, 2007, 02:50 AM   #8
PLC_talk
Member
India

PLC_talk is offline
 
Join Date: Oct 2006
Location: p
Posts: 50
Quote:
Originally Posted by Ken M
The TEMP variable is OB70_EV_CLASS (event class) and this will hold one of two values on each execution. It's a byte-length variable and a value of B#16#72 means an outgoing event (clear) and B#16#73 means incoming event (fault).
Regards

Ken
Following OBs do not have outgoing event, jsut one event.
)B 80,83,85,87,88,121,122
How do I reset these OBs which are having similar detection logic?
Any suggestions?
Thanks,
  Reply With Quote
Old January 29th, 2007, 05:01 AM   #9
Ken M
Member
Scotland

Ken M is offline
 
Join Date: Mar 2004
Location: .
Posts: 1,136
I'm not sure about the logical differences between some OBs and others. It may not be appropriate for an OB detecting a software error to have a code for an outgoing event. Would that mean it runs every scan whenever there is no error? Or what about a chain of errors, where an incorrect DB access causes an invalid value in a calculation which leads to an overflow which produces ... how does the CPU know the problem has been fixed? Just because the CPU can execute the code doesn't justify it in judging it to be error-free. But that's maybe getting a bit philosophical! The truth is I don't know.

For others like OB83 (module insertion/withdrawal) there is no concept of a single incoming and outgoing event. There are separate EV_CLASS values for withdrawal of a module, insertion of a module, start of parameterisation of a module, and end of parameterisation of a module. Each of these messages is a significant event in its own right but you can't say in advance which represents the arrival of a fault and which represents the clearing of a fault. If an existing module is unplugged, the withdrawal EV_CLASS value is the incoming event. If a never previously installed module is plugged in, the insertion EV_CLASS value is the incoming event. So both insertion and withdrawal could represent the occurence of a fault, and likewise both could represent the clearing of a fault. Your code has to tell the difference.

The only mechanism I can think of to reset certain alarm conditions you have created in an error OB is to have a 'Reset' FC or FB in OB1 triggered by a common alarm bit. And that common bit would have to be set in every error OB.

Regards

Ken
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 07:24 AM
Ultra 3000 Step / Direction Mode position error wnkook LIVE PLC Questions And Answers 0 August 17th, 2004 08:24 PM
PLC control of stage lights Thesis LIVE PLC Questions And Answers 3 June 21st, 2004 10:44 PM
Creating a register array to sequence rsdoran LIVE PLC Questions And Answers 15 October 18th, 2003 12:22 AM
Siemens Error OBs Martinvz LIVE PLC Questions And Answers 1 July 17th, 2003 12:11 PM


All times are GMT -4. The time now is 09:35 PM.


.