Old July 19th, 2018, 03:08 PM   #1
einstein_g
Member
United States

einstein_g is offline
 
Join Date: Jul 2018
Location: Cambridge
Posts: 20
PLC IP Address/OPC

I'm very new to PLCs and therefore, OPC. I have a MicroLogix 1000 (Allen Bradley) PLC, which I'd like to connect to an OPC server (KepserverEX) running on my computer.

To connect to the PLC, it obviously needs an IP address assigned, and I need to know what this IP address is.

Do I need to run a DHCP/BOOTP sofware on my PC? Do I need an Ethernet switch in between the PLC and the PC, or an Ethernet crossover cable to connect the PLC to the computer?

Last edited by einstein_g; July 19th, 2018 at 04:03 PM.
  Reply With Quote
Old July 19th, 2018, 03:19 PM   #2
boneless
Lifetime Supporting Member + Moderator
United States

boneless is offline
 
Join Date: Feb 2008
Location: OKC
Posts: 1,459
Hello Einstein,


Welcome to the forum!


Yes, I believe you will need the software to change the IP address of the device.



No you do not NEED a switch, as long as the IP addresses are within range, you should be able to just connect the two devices. With or without switch.
  Reply With Quote
Old July 19th, 2018, 03:25 PM   #3
Sapper307
Member
United States

Sapper307 is offline
 
Join Date: Nov 2017
Location: Maryland
Posts: 92
For newcomers to networking i recommend getting an official Cisco CCNA cert guide book (ICND1 100-105). Of course its specific to Cisco switches and routers, but it also does an excellent job of explaining how and why IP addresses and subnets are determined.

Your OPC server needs the IP address of the PLC, wether or not there is a switch between the two is a matter of system physical architecture. Also generally speaking, automation systems generally don't (but not always)use DHCP... they are usually static IP schemes. So, you most likely need to set the static IP on the NIC of the server machine to a unique IP in the same subnet as the PLC.
  Reply With Quote
Old July 19th, 2018, 03:40 PM   #4
Firejo
Member
United States

Firejo is offline
 
Firejo's Avatar
 
Join Date: Jun 2008
Location: Redmond, WA
Posts: 976
The MicroLogix 1000 does not support Ethernet, only RS232 and RS485. Do you mean MicroLogix 1100? If so you can use the LCD display to find the address assuming someone hasn't set it up so that you can't. Enter the ESC key and then the down button to "Advanced Set" then the "OK" key. Then scroll down (the down button) to "ENET CFG" and then the "OK" button. The IP address should show up.
__________________
Go Hawks!!!
  Reply With Quote
Old July 19th, 2018, 09:00 PM   #5
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,907
Quote:
Originally Posted by einstein_g View Post
Do I need an Ethernet switch in between the PLC and the PC, or an Ethernet crossover cable to connect the PLC to the computer?
Admittedly, I haven't used a Micrologix before, but I haven't cared about what kind of cable to use (patch vs crossover) since I started my current job (8 years). Auto MDI-X is everywhere, and there's no going back.
  Reply With Quote
Old July 20th, 2018, 06:14 AM   #6
EICS
Member
Australia

EICS is offline
 
EICS's Avatar
 
Join Date: Dec 2008
Location: Melbourne
Posts: 75
you can connect to ML1000 by ethernet, but you net a 1761-NetENI ethernet to serial gateway to do it.
  Reply With Quote
Old July 20th, 2018, 09:26 AM   #7
einstein_g
Member
United States

einstein_g is offline
 
Join Date: Jul 2018
Location: Cambridge
Posts: 20
Quote:
Originally Posted by Firejo View Post
The MicroLogix 1000 does not support Ethernet, only RS232 and RS485. Do you mean MicroLogix 1100?
I have the MicroLogix 1000, but I have now just obtained access to a 1400 -- any idea whether the 1400 supports Ethernet without having to purchase a gateway/bridge?
  Reply With Quote
Old July 20th, 2018, 09:30 AM   #8
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,738
Quote:
Originally Posted by einstein_g View Post
I have the MicroLogix 1000, but I have now just obtained access to a 1400 -- any idea whether the 1400 supports Ethernet without having to purchase a gateway/bridge?
Yes the 1400 has a built in Ethernet port
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old July 20th, 2018, 09:31 AM   #9
einstein_g
Member
United States

einstein_g is offline
 
Join Date: Jul 2018
Location: Cambridge
Posts: 20
Many thanks @geniusintraining
  Reply With Quote
Old July 20th, 2018, 09:45 AM   #10
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,738
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old July 20th, 2018, 09:55 AM   #11
einstein_g
Member
United States

einstein_g is offline
 
Join Date: Jul 2018
Location: Cambridge
Posts: 20
I have a newbie follow-up question. In my case above, I want to talk to a single PLC through Ethernet via an OPC server.

What about a case where there are multiple (up to 100) networked PLCs, connected to variable frequency drives?

To talk to these PLCs through OPC, is there a device that I'm supposed to connect my computer to, to gain access to the PLC network?

Last edited by einstein_g; July 20th, 2018 at 09:58 AM.
  Reply With Quote
Old July 20th, 2018, 10:02 AM   #12
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,738
Maybe more details of what you are doing would help

But for the most part, set a (unused) static IP address in your PLC's and the OPC server would look for the address and tags to get your data, can I ask why are you using a OPC server ? are you running a SCADA or HMI or are you just looking to communicate to the PLC? are you using RSLinx as your OPC?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old July 20th, 2018, 10:11 AM   #13
einstein_g
Member
United States

einstein_g is offline
 
Join Date: Jul 2018
Location: Cambridge
Posts: 20
I initially just want to communicate with a single PLC via a KepserverEX OPC server.

Eventually, I'd like to looking into getting whatever data I can obtain from VFDs connected to a network of PLCs.

Communicating with a single PLC seems straightforward -- I can just connect the PLC to my computer via an Ethernet cable.

I'm just not sure how I would communicate with individual PLCs in a network of many PLCs i.e whether I need to connect to this network via an intermediary device.
  Reply With Quote
Old July 20th, 2018, 10:35 AM   #14
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,738
As long as they are on the network and have the correct IP address (you also) you should be able to connect using RSLinx for programming

I have used Kepserver in the past for a couple applications and its not that bad to setup and get running the HMI I was using was RSView, I also had a RSView app with RSLinx OEM as the OPC and both ran good

What is your app that you need the OPC?
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old July 20th, 2018, 10:45 AM   #15
harryting
Lifetime Supporting Member
United States

harryting is offline
 
harryting's Avatar
 
Join Date: May 2002
Location: Puget Sound
Posts: 1,845
It depends. You have to elaborate a bit more on what your intentions are.

For example, you mentioned OPC but saying OPC doesn't tell us what it's used for. Is it used to serve a HMI or talk to another system or device?

Speaking in general. You talk to a specific PLC by setting up a pointer of some kind. In OPC, it's generally called a TOPIC. A TOPIC points to a specific device in an OPC server. A device sit under a CHANNEL. A channel configs the port and protocol.

To tell your program to talk to a PLC the format is in the form of :

OPC Server-Topic

Topic consists of Channel and Device.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
More questions about RSemulator, PLC network, and career path... timcph2008 LIVE PLC Questions And Answers 0 March 8th, 2018 11:04 AM