AB digital fast & normal input?
theripley
Jul 2008
laguna
545
Sorry for this very naive question.
I'm not supposed to post this, but the AB tech team here in my area are out of reach.
I will be using 1766-L32BWA, on the catalog it says, 12 digital fast input, 8 digital normal input & 12 relay output.
What does the fast & normal means? Why are there more fast than normal input?
The 'fast' inputs can be used as inputs to the high-speed counters (HSCs). They can all be used as 'normal' inputs if you aren't using the HSCs.
-Eric
Another question, if I will be connecting 1766-L32BWA to panelview plus 2711P-T6C5D - is cable 1585J-M8CBJM-5 the correct cable to use.
This is as recommended by the supplier, but I am in doubt. Please help.
Allen-Bradley sells a variety of Ethernet cables. Some are very ordinary, and some are special (600V insulation, high-flex, shielded, etc).
Part number 1585J-M8CBJM-5 is a fairly ordinary 5-meter Ethernet cable with a PVC jacket.
That specific model of PanelView Plus has only RS-232, not Ethernet. You will need to connect it to the MicroLogix 1400 Channel 2 with a "straight through" serial cable.
The 2711-NC13 is a "straight through" serial cable sold by A-B for this application. Any straight-through DB9F - DB9F serial cable will work.
You could also use a serial cable to Channel 0 of the MicroLogix 1400, but I'm not certain of that part number.
Kindly check my simple (hand sketched) lay-out. Is this correct?
What's purpose of the FAST INPUT MODULE EL1202 | 2-channel digital input terminal 24 V DC, TON/TOFF 1 µs If the maximum PLC Cycle is 50 µs...
2,557
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
437
I have a PLC type PM856 from ABB with some I/O modules and I get an error from the Digital Inputs model type DI801. The unit status shows error...
264
I am monitoring two BMXDDO3202K digital outputs for their behaviour, they are each for opening and closing, and so the on time affects how far the...
285
On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877. However, I checked with a Fluke, injecting...
890