On the laser displacement sensor now connected to my PLC, the manual says 4mA=643 and 20mA=64,877.
However, I checked with a Fluke, injecting milliamps and 4mA was 0 and 20mA was 27,648.
So how can 20mA be 64,877 for this sensor?
Image to follow...

IMG_20230620_163820.jpg
 
Last edited:
The values on your datasheet pic are internal in the sensor.


They don't know which PLC you are using, some are 12 bit and others 16 or 32 bit.


I have seen 20mA read 4098, 12,000, and 32766 in different PLC's



The PLC manual for the analog input should say what that PLC has for 4mA and 20mA, or hook up a calibrator when online and see what it actually reports.
 
The values on your datasheet pic are internal in the sensor.


They don't know which PLC you are using, some are 12 bit and others 16 or 32 bit.


I have seen 20mA read 4098, 12,000, and 32766 in different PLC's



The PLC manual for the analog input should say what that PLC has for 4mA and 20mA, or hook up a calibrator when online and see what it actually reports.
Ah understood thanks.
I recognise that magic number of 4098 - it's used on Mitsubishi PLCs.
I'm using S7-1200.
Cheers
 
The 64k value is the internal value of the sensor in 16 bits (65535).
Siemens measures up to 27648. That value should be present when you hook the sensor up to the analog input (if its at maximum).
 
The 64k value is the internal value of the sensor in 16 bits (65535).
Siemens measures up to 27648. That value should be present when you hook the sensor up to the analog input (if its at maximum).

At the risk of Too Much Information...

27648 represents 100% of the process value when measuring voltage, current, or resistance (in your case, 20ma). The card will return a value up to about 111.8% of the max, up to 32787. Diagnostic reporting is generally available for values that exceed this limit (Overflow).

Unipolar voltage/current/resistance measurements have a floor (zero percent) of zero, while bipolar measurements have a floor (negative 100%) of -27648.

Unipolar and bipolar are also referred to as Symmetrical and Asymmetrical, respectively, in Siemens documentation.
 

Similar Topics

In OB1, I'm monitoring some values (first pic). The values are what I expect. At the same time, I'm monitoring the same values in the DB where...
Replies
1
Views
651
I'm from a Mitsubishi Q-series background so excuse my ignorance. In Mitsubishi world, in my experience your Mbits (booleans) are just M1, M2...
Replies
20
Views
2,794
I am currently am in a PLC class and need urgent help on how the ladder logic would be laid out. I understand how to get the traffic lights to...
Replies
19
Views
446
Hello, If the date on the license manager of tia Portal has expired, can I still work with it? or is this just to keep the program up to date...
Replies
7
Views
210
Does anyone know why my one string is displaying this way? It is causing issues with my HMI displaying it.
Replies
4
Views
266
Back
Top Bottom