The values on your datasheet pic are internal in the sensor.
They don't know which PLC you are using, some are 12 bit and others 16 or 32 bit.
I have seen 20mA read 4098, 12,000, and 32766 in different PLC's
The PLC manual for the analog input should say what that PLC has for 4mA and 20mA, or hook up a calibrator when online and see what it actually reports.