Panelbuilder32 doubts

EmmanuelM

Member
Join Date
Mar 2023
Location
El Paso Tx
Posts
4
Hi guys I'll appreciate for your support.

I want to know if there is a way to change the text of a label depending of the numeric value of a tag in the PLC


Micrologix1400 PanelView300
N7:0 = 0 ---> 43602E
N7:0 = 1 ---> 42658E
......

thanks
 
Welcome to the Forum!

Yes, you should be able to use a multi-state indicator in Panelbuilder32 to get that result. That is, so long as the text is static and will not frequently change to something else. You can have more than two values and associated texts if needed and you could make the text dynamic with a little more work.
 
Thank you guys it is exactly what i was looking for.

No it will not change frequently just one or twice per day when the operator change the part number.
 
Thank you guys it is exactly what i was looking for.

No it will not change frequently just one or twice per day when the operator change the part number.

The value of N7:0 will change a couple of times per day, right?

Not the text of "43602E" and "42658E", right?

N7:0 could change a thousand times per day, no problem, as long as the two associated texts stay the same, the multistate indicator with static text will be fine.
 

Similar Topics

Hello guys , im new at plc. i have a few questions hopefully someone can help me out. i extracted from an old panelview550 a pba file and...
Replies
12
Views
1,429
I can't find what laptop I have our PanelBuilder32 application and license on. And Rockwell no longer supports it. Can someone please update 1...
Replies
5
Views
1,627
A tech at a remote facility had a PV550 **** out (Err 690 DH+ hardware failed). He took it out and sent it to me, and going by the label on the...
Replies
1
Views
1,256
I recently started getting "corrupted or low disk space" errors on all my backup panelbuilder32 files seemingly out of no where (been running ver...
Replies
2
Views
1,596
I am attempting to mix old with new. I have a 1400e HMI that is communicating to a plc5 via DH+. I need to set the HMI up to read some of its...
Replies
5
Views
2,403
Back
Top Bottom