FT application issue

nievesdelimon

Member
Join Date
Mar 2018
Location
Queretaro
Posts
39
Hi,


Earlier today an application already loaded onto a Panel View stopped working properly. All the go to display buttons stopped working. After turning the device off and on again the buttons were working, but every indicator displayed Error as if their respective tags were wrong; about thirty minutes later the situation went back on its own to go to display buttons not working and connections being ok.



After uploading and restoring the application I verified the buttons were configured correctly.


Does anyone know what might be happening and how to fix it?


The PV and application were working fine yesterday. :confused:
 
Do you have a global connection set for Remote Display Number? If that value is non-zero (usually read from the PLC) then screen navigation via the HMI is locked.
 

Similar Topics

Recently, I fresh install Win10 system, and install FT studio 8:00. when I use its Application Manager Restore runtime application to Restore a...
Replies
4
Views
944
I have an FTView SE network station application ver 10. I am having problems with the alarm banner. The alarm banner is showing only one alarm...
Replies
1
Views
1,449
A customer called us on-site to look at a machine with a Modicon TSX3721001 PLC talking to a Modicon XBTF034510 HMI. Initially, the HMI wouldn't...
Replies
8
Views
3,912
We had a HMI fail over the weekend. The application was developed in version 7 environment. We are currently running version 10 Studio and the...
Replies
13
Views
2,525
Hi all, some one can help me with a restore on Rockwell Factory Talk Transaction Manager? FTTM V10.10, run at Win7 64, Solidcore installed and...
Replies
1
Views
3,005
Back
Top Bottom