Safe-pak relay

unsaint33

Member
Join Date
Sep 2019
Location
MInnesota
Posts
118
I had to replace a Safe-pak relay, which is an intrinsically safe switch relay (Class I, Div 1). However, when I bench test the bad relay and the good relay, I get the same result on the output. The switch side has two terminals for the sensor input. The output side has three terminals (L1, N, Output1). I always get output voltage across N & Output1, whether I jumper the two input terminals or not. I guess an intrinsic relay doesn't work like a normal relay does. Is there a special way to bench test one of these relays to see if it's good or not?

safepak.jpg
 
Do you have the load terminal connected to anything? I'm guessing the output is a solid state device. If the load terminal is not connected an an actual load you are likely just measuring the leakage current through the output driver.

Keith
 
You were right Kamenges. I used a small pilot light as the load and the light came on and still didn't change with the input change. But when I used a contactor as the load and it did change with the input change. Thanks for your help!
 

Similar Topics

Can somebody share the AutroSafe configuration Tool C4.11.4 Thank you
Replies
1
Views
110
I have a GuardLogix PLC with safety inputs of HMI, Estops, Light Curtains, and Gates. Is it considered safe for the safety program to monitor the...
Replies
11
Views
782
We have an existing VSD where a three phase circuit breaker feeds the drive, and two phases also tee off to a contactor, which is energised to...
Replies
12
Views
1,485
Hi, I'm trying to understand a couple of things with a feedback signals that are used in a SRP/CS that I'm working with. Quick disclaimer: I'm...
Replies
2
Views
535
Back
Top Bottom