Old September 13th, 2018, 04:18 AM   #1
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
Connecting the DC-bus of 2 VFDs.

Hi !

I have an application where a vibratory conveyor is driven by 2 agitators.
In order to change the transport direction slightly (for sorting the material on the conveyor), the agitators are driven by VFDs that drive the motors at a slightly different frequency (f.ex. 49.5 Hz and 50.5 Hz). That cause the agitators to run at the same speed (due to the mechanical coupling), but a difference in the angle, which in turn causes a slight angle of the conveyors transporting direction.
Since one agitator is essentially driving and the other braking, the braking VFD has to send a lot of energy to a brake resistor.
This all works OK, but the brake resistor has to be much larger than normal, since it has to bleed off energy constantly rather than only when stopping.
This in turn also means I do not have much room for adjusting the frequency, since the resistor may overheat (despite being dimensioned much greater).

So I am pondering if it could pay off to connect the DC-bus of the 2 VFDs.
The idea being that the braking VFD sends the energy to the driving VFD, and thus do not have to bleed it off in the resistor.
I have heard of this principle, but I have no experience, and I would like to hear from anyone with experience or links to instructions regarding this.
Anything to be aware of ?
The VFDs are Siemens G120. Do some parameters have to be adapted when connecting the DC-bus ?
__________________
Jesper
3 strikes and you're out

Last edited by JesperMP; September 13th, 2018 at 05:06 AM. Reason: clarified as described in post below.
  Reply With Quote
Old September 13th, 2018, 04:47 AM   #2
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,287
I am probably not understanding the problem correctly, but why would a different supply frequency cause the motors powered by VSDs to run any differently? There isn't any direct connection between the speed of a VSD supplied motor and the frequency of the supply.
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old September 13th, 2018, 05:05 AM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
The VFDs output frequency to the motors is different.

I guess the way I phrased it, it is not clear that I meant the supply to the motors, not the VFDs.
I have edited the 1st post to make it clear.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old September 13th, 2018, 05:35 AM   #4
chud
Member
South Africa

chud is offline
 
chud's Avatar
 
Join Date: Oct 2007
Location: KALAHARI
Posts: 889
Good article regarding the different methods.
https://www.motioncontroltips.com/br...-regeneration/

Have not personally done this because in case where needed we normaly use siemens AFE drives which regen back into the mains
  Reply With Quote
Old September 13th, 2018, 05:56 AM   #5
Lynx777
Lifetime Supporting Member
United States

Lynx777 is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 74
Maybe this can be of use.
http://literature.rockwellautomation...t002_-en-p.pdf
  Reply With Quote
Old September 13th, 2018, 06:22 AM   #6
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
Thanks guys.
I am studying these right now.

1st question. In the http://literature.rockwellautomation...t002_-en-p.pdf, on page 54 (and other pages) what does the "Back-to-back diodes that are required for proportional current sharing" actually do ?
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old September 13th, 2018, 06:38 AM   #7
ggc
Member
Australia

ggc is offline
 
Join Date: Apr 2007
Location: Queensland
Posts: 55
I have experienced the downsides of connecting the DC bus of multiple VFDs, the end result is quite catastrophic, and the smell (aka "the stench of failure") stays with you for a long time. The big question that the drive manufacturers seem to forget, if there is a fault on the DC bus of one drive, how will that energy be dissipated before it reaches the next drive.

Case 1: Machine with 10 VFDs connected to a common bus, no protection between drives. 24v DC power supply was undersized, under certain conditions 24V supply would dip enough that drives would go into fault and all try to discharge their capacitors through the same DC bus. First time it occurred, 8 dead drives. We stopped counting after 30. Luckily machine was under warranty, but when the manufacturer is delivering VFDs by the pallet via airfeight, it's time to rethink the design.

Case 2: Machine with 2 VFDS sharing common DC bus, this time seperated by high speed semiconductor fuses. Unfortunately, fuses were not fast enough, 2 dead drives instead of one, and then establishing the root cause of the fault becomes signifcantly harder.

On the flipside, we have 4 other machines from the same manufacturer with same series of VFDs mentioned in case 1, each machine has 3 drives sharing a DC bus with no segregation between drives, and we haven't has a problem.
  Reply With Quote
Old September 13th, 2018, 07:16 AM   #8
JRW
Member
United States

JRW is offline
 
JRW's Avatar
 
Join Date: Jun 2002
Location: Upstate South Cackalacky
Posts: 1,678
Jesper
PM240-2 power units?
Part numbers ?
  Reply With Quote
Old September 13th, 2018, 07:28 AM   #9
sbaum
Member
Canada

sbaum is offline
 
Join Date: Mar 2009
Location: Ontario
Posts: 123
I have done a common DC bus link similar to the 'Chapter 6 - Piggy-back configuration' example in the Rockwell document that was previously posted. This setup was with 2 ABB ACS550 drives. One drive with AC supply, then the 2nd drive was connected via the DC bus.


On this particular machine there is a large (70hp) driven motor and a smaller (20hp) braking motor. It was known that that the smaller motor would always be in regeneration, but regardless we sized the larger drive for 90hp to ensure the 'front end' of that drive could handle any possible load it would encounter.
We used a high-speed DC fuses in the bus link.
  Reply With Quote
Old September 13th, 2018, 08:01 AM   #10
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
gcc, I will probably install semiconductor fuses in the DC circuit.

JRW,
6SL3224-0BE27-5AA0 PM240
6SL3244-0BB12-1FA0 CU240E-2 PN
6SE6400-4BD16-5CA0 Brake resistor
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old September 13th, 2018, 08:08 AM   #11
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,287
The drive knows when it is braking, isn't there anyway to use that to trim the speed of the drive?


edit:

Hadn't though that through, you would have to trim to speed of the second drive.
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old September 13th, 2018, 08:11 AM   #12
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
The two agitators must be driven with different frequencies to get the desired effect.
It is impossible to not have one VFD braking when the other is driving.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old September 13th, 2018, 08:31 AM   #13
Lynx777
Lifetime Supporting Member
United States

Lynx777 is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 74
Quote:
Originally Posted by JesperMP View Post
Thanks guys.
I am studying these right now.

1st question. In the http://literature.rockwellautomation...t002_-en-p.pdf, on page 54 (and other pages) what does the "Back-to-back diodes that are required for proportional current sharing" actually do ?
Check out pg. 133. The manufacture of the modules has some good info on what they do. Here is a manual for one of them - http://www.bonitron.com/PDFs/Manuals...N_VALL_02f.pdf
  Reply With Quote
Old September 13th, 2018, 08:55 AM   #14
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,397
Quote:
Originally Posted by Lynx777 View Post
Check out pg. 133. The manufacture of the modules has some good info on what they do. Here is a manual for one of them - http://www.bonitron.com/PDFs/Manuals...N_VALL_02f.pdf
The schematics in the AB PDF just says the back-to-back diodes are needed. I cannot see what the illustrated parallel diodes in opposing directions actually do.
The schematics in the bonitron pdf page 15 is different to AB, but it makes sense to me.
I am guessing that bonitrons description is the correct one.

edit: No wait, the bonitron illustration does not apply to my case.
I have several VFDs as in the AB PDF page 54, not with socalled "regen modules" as in the bonitron PDF page 15.
I am still mystified as to what this diode module does, and how I should apply it in my application, and if I even need it.
__________________
Jesper
3 strikes and you're out

Last edited by JesperMP; September 13th, 2018 at 09:30 AM.
  Reply With Quote
Old September 14th, 2018, 06:08 AM   #15
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,287
Or you could look at Regenerative Braking. I know little about the Siemens G120 but a quick search seems to say that you can add modules to give regenerative braking.
https://www.industry.usa.siemens.com...ve-drives.aspx
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1394C-AM07 dc bus fuse technolog LIVE PLC Questions And Answers 0 January 10th, 2018 02:46 PM
Supply vfd with dc power lesmar96 LIVE PLC Questions And Answers 31 August 24th, 2017 05:08 PM
Nominal bus voltage for Kinetix 5500 @490VAC ? Ken Roach LIVE PLC Questions And Answers 11 June 26th, 2017 11:41 PM
Automation Direct PLC's Opinions Duwop LIVE PLC Questions And Answers 44 October 11th, 2007 09:35 AM
PLC S7300 Bus Connector g_simons LIVE PLC Questions And Answers 2 June 10th, 2002 08:57 PM


All times are GMT -5. The time now is 08:31 AM.


.