Text string with bunch of questions

ziyaddin2015

Lifetime Supporting Member
Join Date
Nov 2019
Location
USA
Posts
84
Hi All,
I have a problem with HMI where the tag string shows a bunch of question marks. I am not sure where to go from here?? I believe someone else had fixed a similar issue on the other line saying he updated UDT. Any suggestions will be greatly appreciated. Thanks

20200927_111700.jpg
 
That appears to be a Rockwell FTView ME HMI, and it may mean that the tag associated with those "?" is longer in length that what the graphic is currently set up for. I.E. Tag is 20 characters long but HMI reference is only 17 characters long.
 
That means that the tag that the HMI is trying to display is not found in the PLC.

When this happens to me, either I mistyped the tag in the HMI display or changed the tag name or UDT structure in the PLC.

The asterisk on the end says the display is set to more characters than there is room for.
 
Do I need to download to HMI in the case where the tag was mistyped? I ll ckeck out UDT structure in PLC as well. Thank you all.
 

Similar Topics

I am creating a global object in FTView SE 13. I want to have a string read from the PLC and display (in this case the tagname). So lets say...
Replies
4
Views
169
Long story short, I am creating a display to display an array of Strings from PLC [topic]VarStrA_RPHD.Desc[VarStrB] totally 100 strings...
Replies
1
Views
1,403
Hi all, I have a customer that is asking for a recipe of 200 recipes to be sorted. I'm trying to do this by way of a bubble sort. Basically my...
Replies
18
Views
3,464
So in Ignition I can make a Tag have a datatype String, or a datatype Text. I poked around in the docs and couldn't find an explanation for the...
Replies
3
Views
2,061
Codesys 3.5 SP15: So I created a screen with a Combo Box the combo's value is set to a Instance of an ENUM, I have a textlist configured too...
Replies
1
Views
1,444
Back
Top Bottom