Noise Problem - NI cRIO, Control Techniques Unidrive SP

System:
  • Drive: Control Techniques - Unidrive SP (Panel Mount)
  • Controller: NI cRIO
  • Power: Whole system runs off of a 3 phase 480V plug. There is a transformer for 120V that powers a few accessories and a 24V supply. VFD is run directly of the 480.
  • May be relevant, entire system is somewhat portable. Panel is on a steel stand that sits next to the machine. All grounding must be through ground prong on 480V plug.

Problem: Severe "bouncing" of several different input signals (mV/V and 4-20mA) whenever the drive is active. Only when the drive is told to run, even if at 0 speed. As soon as drive is stopped (but still powered) signals return to acceptable levels.

Things I've tried:

  • Sent signal with process meter - worked fine.
  • Signals cables are shielded only on panel side.
  • Ran signal cable(4-20mA) completely outside of panel and trays, no change. Moved 24V supply out of panel, laid on floor temporarily, no change. These make me think this is not radiated EMI.
  • Because different types of signals are effected, I suspected noise at power supply. Measured huge (>10V) periodic spikes between +24V and 24VCOM.
  • No "direct" connection between VFD and 24V system. Only connection is 24V sourced from drive through a Guard Master safety relay contact back to the drive, and chassis ground.
  • Moved power supply away from VFD, isolated power supply, tried another power supply all with no change. Seems like power supply is OK.
  • Replaced drive enable through safety relay with a jumper (temporarily) so that only thing shared between the drive and the 24V system is chassis ground. Problem persisted.
  • This made be suspect noise on chassis ground. Measured between chassis ground and earth ground from a nearby 120V outlet. Spikes still visible, I think confirming that the noise is present on the entire chassis. I definitely think this severe noise on ground would interfere with the cRIO.
Since the only thing I did not yet isolate between the VFD and 24V system is chassis ground, my next idea is to try taking the panel mount drive completely out of the panel however this may be a bit of a project since it is mounted in a very tight space. Tried removing the chassis ground connection, however I assume it is still grounded through the panel. If this does eliminate the noise, I will need to determine if the drive is faulty or configured properly (I do have a call out to control techniques, have not heard back yet). If it doesn't, then I am still stumped.


Another thing I may try soon is configuring the drive to not source the 24V for the enable signal. Maybe something in the transformer and power supply internal to the drive is the cause? I've attached photos of the scope measurements although I'm not real confident on them. I think I should have been DC coupling, which I did since and is where I measured the much higher spike values (+/- 2.5 - 3 divs at 5V/div). Unfortunately don't have pictures of latest measurement.


Any Ideas? Also, glad to finally make a post here, I've had many problems solved through google searches that lead to threads here over the past few years in this field. Thanks in advance!
Attached Images
File Type: jpg IMG_0647.jpg (39.2 KB, 10 views)
File Type: jpg IMG_0648.jpg (69.7 KB, 10 views)
File Type: jpg IMG_0649.jpg (57.2 KB, 9 views)
  Reply With Quote
Old February 13th, 2017, 05:22 PM   #2
Levi G
Member
Canada

Levi G is offline
 
Join Date: Sep 2015
Location: Alberta
Posts: 39
Did you use VFD cable from drive to motor or just flexible cord? I had this problem once where my light curtain kept tripping falsely when my drive was running till I installed a VFD cable
  Reply With Quote
Old February 13th, 2017, 05:35 PM   #3
ParetosFew
Member
United States

ParetosFew is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 5
It is just flexible cord for each of the three phases and a heavy ground wire. Now that you say that, I recall reading that advice on other issues related to VFD noise. The three phases and ground go through a dedicated piece of seal tight that is grounded, however there is maybe a foot between the VFD connection and where it enters the seal tight.
  Reply With Quote
Old February 13th, 2017, 05:59 PM   #4
osmanjdt
Member
Malaysia

osmanjdt is offline
 
Join Date: Jun 2016
Location: johor
Posts: 108
old motor or new motor?
  Reply With Quote
Old February 13th, 2017, 06:05 PM   #5
ParetosFew
Member
United States

ParetosFew is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 5
Motor is new. New meaning purchased when the project was started ~3 years ago, not run very much at all during that time.
  Reply With Quote
Old February 13th, 2017, 06:31 PM   #6
milldrone
Member
United States

milldrone is offline
 
milldrone's Avatar
 
Join Date: Mar 2005
Location: in the dog house
Posts: 1,288
ParetosFew,

Is your 480 supply floating delta? or grounded wye?
__________________
Vaughn

If you can read this, thank a teacher.
  Reply With Quote
Old February 13th, 2017, 07:10 PM   #7
Patfu!
Member
United States

Patfu! is offline
 
Join Date: May 2014
Location: Vancouver Wa
Posts: 33
I had a similar issue with a 25HP CT drive. The HMI several feet away would go nuts. We switched to shielded cable from the drive to the motor and it fixed the issue.
  Reply With Quote
Old February 14th, 2017, 02:04 AM   #8
ParetosFew
Member
United States

ParetosFew is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 5
Quote:
Originally Posted by milldrone View Post
Is your 480 supply floating delta? or grounded wye?
I hate to admit this but despite reading up on this and vaguely recalling these configurations from school, I'm still not sure how to tell which I have. From what I read I can't tell by the plug alone? It is a 4 pin plug, 3 phases and ground if it helps. I can talk to the electricians that did that service as well.

Quote:
Originally Posted by Patfu! View Post
I had a similar issue with a 25HP CT drive. The HMI several feet away would go nuts. We switched to shielded cable from the drive to the motor and it fixed the issue.
Seeing this recommendation a lot on other VFD noise issue threads. I guess it does make sense that a heavily shielded cable would do much better than just a ground parallel to the 3 phases. I will likely add this to the list of things to change on this machine even if the immediate problem is resolved some other way. Thank you both.
  Reply With Quote
Old February 14th, 2017, 06:54 AM   #9
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 175
I've minimized the motor-lead radiated noise enough a few times by braiding the motor leads. Otherwise, ensure the motor ground is solid and from there, the only molution is VFD cable (shielded).
  Reply With Quote
Old February 16th, 2017, 07:05 PM   #10
ParetosFew
Member
United States

ParetosFew is offline
 
Join Date: Feb 2017
Location: Pennsylvania
Posts: 5
I was able to resolve the problem (mostly) by overnighting a proper VFD cable from control techniques. Also when changing this over I found something odd: the ground that I thought traveled parallel to the motor conductors actually traveled around the machine and connected to some fixed speed pumps and then back to the panel in a different area not through the drive. Obviously I connected the ground inside the VFD cable directly to the drive. The noise on my 4-20mA signals went away, there is still some bounce all the time but it is indistinguishable whether or not the drive is on or not by watching the numbers. I expect some variation in these due to the large pressure range represented.

The mV/V load cells still show some noise (greatly reduced) but I think this is to be expected with a low voltage signal. There is also some suspect cable routing I can change to improve them.

The cable from control techniques is foil braid shielded, and has the three conductors and a ground twisted together. I may even look into high performance belden VFD cable that has "more copper" to help prevent noise leakage, some of them have three uninsulated ground wires that spiral around with the conductors and insulated ground. Thanks to all for their responses and advice.

Last edited by ParetosFew; February 16th, 2017 at 07:11 PM.
  Reply With Quote
Old February 17th, 2017, 04:42 AM   #11
Andybr
Member
United Kingdom

Andybr is offline
 
Join Date: Oct 2004
Posts: 570
The shield part of the VFD cable is just a "nice to have". The important thing is that the ground runs directly from the motor frame to the VFD frame within or directly alongside the drive cable. Everything else is secondary. There are other "non noise" considerations which might dictate the optimum method of running the ground cable so I would recommend following the drive manufacturers instructions but in more than 99% of VFD related noise issues I have had to deal with the culprit has been having a separate route for the ground and drive cables or terminating the ground cable on the panel rather than the drive. With the high carrier frequencies used by modern drives the capacitance of the cables and the motor allows significant leakage currents to flow and these must be cancelled out within the cable installation to avoid noise issues.
__________________
“What are the facts? Again and again and again-what are the facts? Shun wishful thinking, ignore divine revelation, forget what “the stars foretell,” avoid opinion, care not what the neighbors think, never mind the unguessable “verdict of history”–what are the facts, and to how many decimal places? You pilot always into an unknown future; facts are your single clue. Get the facts!”

Robert Heinlein.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Control Techniques SK-drive on profibus Plc_User LIVE PLC Questions And Answers 2 November 4th, 2008 03:01 AM
Control Techniques Unidrive Sp Plc_User LIVE PLC Questions And Answers 1 April 29th, 2008 05:25 AM
Siemens S7 PID Control Problem qee LIVE PLC Questions And Answers 27 May 15th, 2007 10:53 AM
Control logix HSC module problem? huynt LIVE PLC Questions And Answers 1 October 5th, 2005 09:56 PM
GE Fanuc VersaMax PID control problem Shawn Cassidy LIVE PLC Questions And Answers 6 May 16th, 2004 08:10 AM


All times are GMT -5. The time now is 11:02 PM.


.