Hello- i have 200Hp compressor that is operated with a FW Murphy controller. As the unit ramps to speed, the input lights start to flicker and the whole unit goes down annd into alarm. The inputs are tied to ground to complete their circuit. This machine ran for years with no problems. We also burned out 2 controllers in the last 8 months and now can't get the machine to ramp to speed without tripping. the 24V supply has been changed and no fix. Also put a Fluke 87 on Min hold and it seems stable through this occurence. Seems like a ground problem-any ideas??
 
Is this Murphy controller skid mounted along with the compressor? High vibration?

Get your screw driver out and check all connections for tightness.
 
Is there a ground running back to the electrical distribution panel? I know a lot of people love to add a ground rods for individual pieces of equipment. However, creating a difference in potential like that (a ground loop), you can have another piece of equipment in the facility using your compressors ground, and perhaps it is effecting your controller?


Had this problem a number of years ago with a company that had a DC speed control that would go out every 2 months, and they'd replace it with a new one. Turns out there was a ground loop, and a small heating element in another piece of equipment was using that path to leak current to ground, somehow it was effecting the speed controller.

This most likely isn't your problem, but I figured I'd throw my 2 cents in.

Best of luck! Let us know what you find. :)
 
Thanks for the replies. it turned out to be loose RTD wiring inside the head that was messing with the 24V. This in turn was affecting the controller performance. Weird part was the 24V wer enever sagging? O well-it's fixed and i'll store that one in the brain somewhere!
 

Similar Topics

System: Drive: Control Techniques - Unidrive SP (Panel Mount) Controller: NI cRIO Power: Whole system runs off of a 3 phase 480V plug. There is...
Replies
10
Views
4,652
I have a panel that was retrofitted with a Zelio PLC and a 100HP Parker 590 DC drive. The panel has been having trouble for months with the...
Replies
2
Views
1,728
I have a systwem that I set up that uses 2 paddle wheels npn devices and an encoder card. I have a digital meter hooked up that correctly counts...
Replies
22
Views
8,531
So I had a strange problem today that defied what I've learned about data communication. basic setup is: Scanner -> PLC via RS-232 using only...
Replies
7
Views
6,517
Hello, I am running a AMCI SD4840 Stepper Motor drive system with Allen Bradley CompactLogix. Every now and then when a 480VAC motor kicks in on...
Replies
1
Views
592
Back
Top Bottom