Old January 23rd, 2021, 04:04 PM   #1
ganutenator
Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,258
noise

I don't want to state the obvious to those in the know, but I wasn't in the know.
Apparently, the way dc switching power supplies work, they are the cause of most noise.
When I say noise, let me explain.
We were doing an install.
Customer complained that his crescent wrench sparked on the machine and that he got a jolt.
I measure the voltage in ac from the equipment to ground. It was aprox 20VAC.
We both walked back to the panel.
Everything was turned off except for the 24dc power supply.
I was like, bet the ground wire isn't landed.
Sure enough, the electricians had yet to land the ground wire.
  Reply With Quote
Old January 23rd, 2021, 07:57 PM   #2
Holmux
Lifetime Supporting Member
Denmark

Holmux is offline
 
Join Date: Oct 2013
Location: Aalborg
Posts: 228
Nothing beats "transformer + Bridge + Capacitor"

I know you have to look for them, but they are out there.

I even take it a step further, I always start with a transformer using a 2 fase input, giving me a fase and "Neutral" as the output.

I never pull a neutral from the plant into my cabinet.
  Reply With Quote
Old January 23rd, 2021, 10:55 PM   #3
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,996
as an insurance policy, i always connect x2 of the secondary to the control panel. may have nothing to do with your issue, but i have never had or heard of (until now) what you are describing.
what brand power supply was it?
james
  Reply With Quote
Old January 24th, 2021, 02:47 AM   #4
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 2,973
20 vac is not much & probably general pickup could be from anywhere, did you isolate the 24v power ?, did it make a difference?, I once had a panel that was not even wired to any external power or any of the I/O, in actual fact there were no wires at all, a colleague said he had a shock off the panel, it was still on a pallet so checked to earth and got a varying ac voltage of 10-40v but as soon as I put my hand on the panel it dropped to about 10, so it may not be anything to do with the PSU. The other thing is a multi meter is quite a high impedance, so draws little current.
  Reply With Quote
Old January 24th, 2021, 07:59 AM   #5
ganutenator
Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,258
Any solid state power supply causes noise. Back in the day they didn't. But the high frequency switching that they use now does.
The only thing turned on was the 24 vdc pwr supply.
It induced enough voltage on the wires to cause you to get shocked.
Turn it off and it goes away.
Connect the ground and it goes away.
So yes, probably best to go old school w/ the power supply.
Or shield the f*ck out of everything.
Just thought this find would be useful is all.
  Reply With Quote
Old January 24th, 2021, 10:42 AM   #6
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,567
I don't think it would be anything to do with induced voltages. It would be one of the filters that they use to stop noise going back to the supply that was putting volts on to the unearthed earth connection. You can't really blame the Power Supply if the system isn't earthed.

Picture from: https://www.emea.lambda.tdk.com/uk/f...ion.aspx?id=99
Attached Images
File Type: jpg EMI Filter.JPG (16.4 KB, 169 views)
__________________
Knowledge is power, share the knowledge.
  Reply With Quote
Old January 24th, 2021, 12:31 PM   #7
Yacineg
Member
India

Yacineg is offline
 
Join Date: Oct 2020
Location: Guj
Posts: 13
Quote:
Originally Posted by ganutenator View Post
I don't want to state the obvious to those in the know, but I wasn't in the know.
Apparently, the way dc switching power supplies work, they are the cause of most noise.
When I say noise, let me explain.
We were doing an install.
Customer complained that his crescent wrench sparked on the machine and that he got a jolt.
I measure the voltage in ac from the equipment to ground. It was aprox 20VAC.
We both walked back to the panel.
Everything was turned off except for the 24dc power supply.
I was like, bet the ground wire isn't landed.
Sure enough, the electricians had yet to land the ground wire.
Forgive me for a stupid question. It is a 24v DC power supply & he is reading 20V AC from equipment to ground. How is the reading in AC ?
__________________
  Reply With Quote
Old January 25th, 2021, 10:27 AM   #8
ganutenator
Member
United States

ganutenator is offline
 
ganutenator's Avatar
 
Join Date: May 2002
Location: kansas
Posts: 1,258
Quote:
Originally Posted by Yacineg View Post
Forgive me for a stupid question. It is a 24v DC power supply & he is reading 20V AC from equipment to ground. How is the reading in AC ?
Apparently induced voltage turns into AC. Only a SWAG but probably due to the high frequency switching of the power supply.

Additionally, turning on DC braking on the drives does the same thing.

The noise will actually turn the inductive prox's into capacitive prox's.
  Reply With Quote
Old January 26th, 2021, 08:12 AM   #9
Yacineg
Member
India

Yacineg is offline
 
Join Date: Oct 2020
Location: Guj
Posts: 13
Thank you.
__________________
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Servo Amplifier MR-J4 NOISE in power line zai_jnr LIVE PLC Questions And Answers 1 November 13th, 2019 06:09 AM
VFD Noise on Incoming Line JRoss LIVE PLC Questions And Answers 21 October 20th, 2017 11:48 AM
Noise Problem - NI cRIO, Control Techniques Unidrive SP ParetosFew LIVE PLC Questions And Answers 10 February 17th, 2017 04:42 AM
USB noise with a headset surferb LIVE PLC Questions And Answers 5 May 10th, 2008 09:21 AM
VSD Noise Headache lalion LIVE PLC Questions And Answers 6 July 19th, 2007 04:48 PM


All times are GMT -5. The time now is 07:10 AM.


.