I don't want to state the obvious to those in the know, but I wasn't in the know.
Apparently, the way dc switching power supplies work, they are the cause of most noise.
When I say noise, let me explain.
We were doing an install.
Customer complained that his crescent wrench sparked on the machine and that he got a jolt.
I measure the voltage in ac from the equipment to ground. It was aprox 20VAC.
We both walked back to the panel.
Everything was turned off except for the 24dc power supply.
I was like, bet the ground wire isn't landed.
Sure enough, the electricians had yet to land the ground wire.
Nothing beats "transformer + Bridge + Capacitor"
I know you have to look for them, but they are out there.
I even take it a step further, I always start with a transformer using a 2 fase input, giving me a fase and "Neutral" as the output.
I never pull a neutral from the plant into my cabinet.
as an insurance policy, i always connect x2 of the secondary to the control panel. may have nothing to do with your issue, but i have never had or heard of (until now) what you are describing.
what brand power supply was it?
james
20 vac is not much & probably general pickup could be from anywhere, did you isolate the 24v power ?, did it make a difference?, I once had a panel that was not even wired to any external power or any of the I/O, in actual fact there were no wires at all, a colleague said he had a shock off the panel, it was still on a pallet so checked to earth and got a varying ac voltage of 10-40v but as soon as I put my hand on the panel it dropped to about 10, so it may not be anything to do with the PSU. The other thing is a multi meter is quite a high impedance, so draws little current.
Any solid state power supply causes noise. Back in the day they didn't. But the high frequency switching that they use now does.
The only thing turned on was the 24 vdc pwr supply.
It induced enough voltage on the wires to cause you to get shocked.
Turn it off and it goes away.
Connect the ground and it goes away.
So yes, probably best to go old school w/ the power supply.
Or shield the f*ck out of everything.
Just thought this find would be useful is all.
Forgive me for a stupid question. It is a 24v DC power supply & he is reading 20V AC from equipment to ground. How is the reading in AC ?
Apparently induced voltage turns into AC. Only a SWAG but probably due to the high frequency switching of the power supply.
Additionally, turning on DC braking on the drives does the same thing.
The noise will actually turn the inductive prox's into capacitive prox's.
Hello, I am running a AMCI SD4840 Stepper Motor drive system with Allen Bradley CompactLogix. Every now and then when a 480VAC motor kicks in on...
590
Hello Everyone, I hope we are all well. I have an L36ERM with a 1769-OF8C/a driving a 5HP Power Flex 523 speed reference 4-20 mA. With the...
1,836
Good Morning , We have a new Fortress Stealth Metal Detector. About 30' away we have a machine with motors and solenoids on it , Whenever...
2,196
What is the purpose of noise filtering in the power input side of plc. any suggestion/recommended noise filter for GE brand of plc. Thanks
1,482
We worked in a sewage treatment plant and take care of their plc work. They have an issue with noise some of the analog signals in the plant. When...
19
7,074