Well hopefully one of you guys has an answer for me !
I have a 1747-SDN Series B rev 2.01
I want to upgrade the firmware to 6.002
Well this has been going on for 2 weeks now and i am not a lot further forward!
The UK Distributor of AB stuff has just come back to me and said that its not possible and i need to buy a new scanner with the latest FW
I have looked on AB's site and seen the download for the Flash Upgrade for SDN firmware, this doesnt work on my scanner as its below 3.xxx (I think) I get an error SDN not flash upgradeable etc
I have further found on the RA KB that i can buy a firmware upgrade kit F1747-SDN to upgrade my 2.01 SDN...........
Well i ordered this only to be told its not an AB part number (by the distributor) and i need to buy a new scanner!!
Its started to get me going now!
Today i got an email from RA UK tech support that i need to upgrade the FW of the scanner to 3.xxx before i can flash to 6.002, they say thay are going to email me the upgrade to 3.xxx
Well apart from 2 weeks down the line and being p1ssed off can anyone tell me the correct answer / method or shall i just post my scanner to the UK Distbributor in pieces ?
I have a 1747-SDN Series B rev 2.01
I want to upgrade the firmware to 6.002
Well this has been going on for 2 weeks now and i am not a lot further forward!
The UK Distributor of AB stuff has just come back to me and said that its not possible and i need to buy a new scanner with the latest FW
I have looked on AB's site and seen the download for the Flash Upgrade for SDN firmware, this doesnt work on my scanner as its below 3.xxx (I think) I get an error SDN not flash upgradeable etc
I have further found on the RA KB that i can buy a firmware upgrade kit F1747-SDN to upgrade my 2.01 SDN...........
Well i ordered this only to be told its not an AB part number (by the distributor) and i need to buy a new scanner!!
Its started to get me going now!
Today i got an email from RA UK tech support that i need to upgrade the FW of the scanner to 3.xxx before i can flash to 6.002, they say thay are going to email me the upgrade to 3.xxx
Well apart from 2 weeks down the line and being p1ssed off can anyone tell me the correct answer / method or shall i just post my scanner to the UK Distbributor in pieces ?