Hi all,
I am planning on installing a AB 1794 point IO system using the ethernet 1794-AENT and 7 IO modules connected to a compactlogix L35E. The point IO will be up to 200m from the logix,will this work at this distance,and is there a recommended cable type(cat 5,5e,6)Thanks..
Typically shielded CAT 5e is recommended. I have in my notes (I'm sure I got it from an AB or standard ethernet recommendation as I didn't cite a source) that the maximum length is 100 meters.
If you need to run 200m then the recommended solution is to use fiber converters. Check out the 1783-ETAP1F or 1783-ETAP2F.
The distance you can run twisted-pair Ethernet is an ordinary limit of Ethernet technology; it's not vendor-specific to A-B. 200 meters of twisted-pair wire will not support an Ethernet link.
You need a switch or repeater in the middle of the run, or you need to run another type of media. Typically long runs are done with fiber optic media and a media converter. I like these units from N-Tron: http://www.n-tron.com/products_sub.php?type=MC
Thanks for the replies.Looks like fibre optic is the way to go. When you set these up in RSlogix 5000 do you still map the 1794-AENT to the ethernet port or the fibre converter?
The IP infrastructure is transparent to RSLogix 5000; all it knows about is the 1734-AENT adapter out there.
There could be Ethernet cable, fiber-optics, WiFi, cable modems, cell phones, or carrier pigeons in between. As long as the packets arrive in a timely fashion, the controller doesn't know what carries them.
Anyone know off the top what the maximum cable length should be between a compact logix controller and some point I/O? I have 10 meters in my...
1,599
Does anyone know the part # for Allen Bradleys Point to Point cable? This cable is used for panelbuilder 32 to panelview Rs232. Thanks!!
3,175
We are having issues with our viewpoint server randomly crashing and only loading the error page if anything at all. It lives on 3 servers all of...
57
Good morning, I have a question regarding some point I/O modules. We use 1734-IE2V modules to measure the tension of a fiber, but we have quite a...
83
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
98